This week I was at a plant when a machine blew one of its main 100A fuses. I was helping troubleshoot this problem. I started by ohming the lugs on the main disconnect to ground and measured 0.3 ohms. We turned off all circuit breakers to start isolating the source of the short to ground and narrowed it down to a 60Kva 3 phase transformer. The transformer had a 480V delta primary and a 400V Wye secondary. The neutral on the secondary was grounded. The primary connections ohmed 0.3 to the secondary's neutral.
After disconnecting the transformer it still showed the 0.3 ohms between any of the connections on primary and secondary. Because of this I concluded the transformer was bad and had a break down in insulation between a primary and secondary winding.
We went to the stock room and found another transformer that was the same, but just larger. I made the same resistance measurements between primary and secondary and it also showed 0.3 ohms. Because of this I backed off my conclusion of the bad transformer and had them wire up only the primary side so we could power it up and check the voltage on the secondary.
Well, it turned out the main fuse blew again and the transformer started to catch fire in the first winding. The maintenance men then took a transformer from the stock room and installed it. That resolved the problem and the machine was back running.
So my question is, how could I measure any kind of resistance between the primary and secondary of a 3 phase transformer? Would that mean the primary 480VAC has a path to ground since the secondary neutral is grounded?
I followed the connections on the transformer to see if it was internally wired as an autotranformer, but could not see any such connections. Also the electrical schematic showed it as a typical transformer with the primary and secondary isolated.
This also brought to my mind of how to properly check such as transformer when both the bad one and the one in the stock room checked the same when using a standard meter to measure resistance?
After disconnecting the transformer it still showed the 0.3 ohms between any of the connections on primary and secondary. Because of this I concluded the transformer was bad and had a break down in insulation between a primary and secondary winding.
We went to the stock room and found another transformer that was the same, but just larger. I made the same resistance measurements between primary and secondary and it also showed 0.3 ohms. Because of this I backed off my conclusion of the bad transformer and had them wire up only the primary side so we could power it up and check the voltage on the secondary.
Well, it turned out the main fuse blew again and the transformer started to catch fire in the first winding. The maintenance men then took a transformer from the stock room and installed it. That resolved the problem and the machine was back running.
So my question is, how could I measure any kind of resistance between the primary and secondary of a 3 phase transformer? Would that mean the primary 480VAC has a path to ground since the secondary neutral is grounded?
I followed the connections on the transformer to see if it was internally wired as an autotranformer, but could not see any such connections. Also the electrical schematic showed it as a typical transformer with the primary and secondary isolated.
This also brought to my mind of how to properly check such as transformer when both the bad one and the one in the stock room checked the same when using a standard meter to measure resistance?