Automation Direct PID
swayne76
Jan 2012
ohio
43
Having some trouble tuning a PID loop in Do-more designer. I am using an H2-DM1E with a F2-THM module. Has anyone had any luck tuning a heat loop with this software? I am getting quite a bit of overshoot.
Assuming your Thermocouple module is F2-04THM.
Check memory allocations to make sure you left enough room for variables.
Start with "P" only. What is "P" now?
Repeat cutting it in half and try again until you eliminate overshoot.
P is set at 5. I and d are at zero. I have noticed as I approach setpoint the loop doesnt pull back the output. I manually lower the "bias" and the loop begins to pull back and stabilize. Any insight on how the "bias" works. The manual doesnt go into much detail.
I am doing a wire spooling application using an Automation Direct D-260 cpu, F2-8AD4DA-2 16 bit 8 ch in / 12 bit 4 ch out 0-10 vdc board. The...
5,408
OK, this is the first time I have had a need to use a PID loop with an Automation Direct PLC. Hardware : D4-450 with updated firmware V3.3...
5,596
Has anyone used the automation direct plc to do water cooling of an extruder barrel? Heating is no problem but setting up a heat & cool zone is...
4,462
Hello, I have an automation direct d2 262 plc and C-more HMI EA9T6CL-R. I need to prepare a program, scheduled to be performed on a future date. I...
119