Panel View 600 DH485 comm.

jayala

Member
Join Date
Jun 2004
Location
CA
Posts
17
HI
I have been trying to program a Panel View 600 CAT#2711-T6C5L1
I'm using a comm. cable 2711-NC13 .when I try to download a simple push button I get an error node no found so I change the node I delete the push button and download a goto screen function
and it ask for comm.setup DF1, network,memory. The only one that works was the netwok setup I can see that the download is in effect without problem but if I try to download a push button it doesn't allow me to do so. :(

Please any help would be very apreciated

John A.
THX
 
As soon as the program is loaded to the PanelView it will try to find the nodes/addresses that are attached to all objects on the visible screen.

If it cannot find them it comes back with a "node not found" error.

Look at the address and node attached to the pushbutton object. The PanelView will want to find the a PLC on the DH485 network, with the correct node number, and with the datatable address created within it's memory.
 

Similar Topics

Hi Everyone, I am new to the site and to plc programing. Always been the guy trouble shooting around them. I have a Panelview 600 2711-b6c8...
Replies
6
Views
1,313
Hello everyone I have a PanelView Plus 600 that is acting up. To be able to go into our manual operations of the machine it runs, a small fluid...
Replies
18
Views
4,964
Dear expert /Group members Good day to your Does anyone have this problem? Problem explanation as below :- Thanks in advance
Replies
1
Views
1,043
Hello everyone, im new in Allen Bradley World, i alredy know how to use factory talk view and with manager i have alredy upload all runtime...
Replies
1
Views
1,680
Trying to connect an old panel view 600 to a control logic processor over device net I have devicenet connected but can't seem to address the...
Replies
7
Views
1,641
Back
Top Bottom