OK guys I have been out of the game for several years, but I am sure it will come back to me. I have a 5/04 CPU that is flakey. What is everyone using to connect to the mini round connector. In the past it used to be a PM02 cable, but I am seeking the best solution today. (USB to 5/04 round programming port)

As always you help is greatly appreciated.
Ken
 
In the past it used to be a PM02 cable, but I am seeking the best solution today. (USB to 5/04 round programming port)

Hi Ken,

The PM02 is for a MicroLogix PLC, the round mini din on a 5/04 is DH+ and you will need a 1784-U2DHP cable if you are looking for USB to that port, we sell a aftermarket version that works great and is 1/3 of the cost

If you are looking for the cheapest way just use a USB CP3 cable that will connect to the DB9 port on the 5/04

Mark
 
Thank you for the correction

I told you it had been a long time. Thank you for the correction. Which cable brand do you sell. Meanwhile I will take a quick look on your website.

Ken
 

Similar Topics

I'm trying to read/write to an SLC5 with a ControlLogix L71 V35 plc that fails. The exact same code works on an L82S with V32. Is there a known...
Replies
9
Views
70
I'm ashamed to admit this but I've never had to replace a battery in a SLC. Some how been able to skip that task in all my years. So yesterday...
Replies
8
Views
209
I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
Replies
48
Views
792
Hello PLC friends. I've been going through a saga of diagnosing and fixing an old PLC setup that I inherited. I am learning as I go. Initial...
Replies
14
Views
298
I had a 5/01 CPU give a CPU Fault. It lost the program and I was not able to establish communication with it. I replaced it with a 5/03 we had in...
Replies
3
Views
110
Back
Top Bottom