level switch vs pressure switch

Dear,

For protecting the pump against dry running, it is better to use low level switch in the tank or pressure switch on the suction side?

I tend to go for low level switch in the tank to protect the pump from dry run, please advise of any thought.

thank you!

charbel
  Reply With Quote
Old July 25th, 2014, 05:49 AM   #2
nonuke
Member
Portugal

nonuke is offline
 
nonuke's Avatar
 
Join Date: Sep 2005
Location:
Posts: 840
Why not use a flow switch after the pump of the type: IFM - SI5000
  Reply With Quote
Old July 25th, 2014, 08:59 AM   #3
John Soltesz
Member
United States

John Soltesz is offline
 
John Soltesz's Avatar
 
Join Date: May 2007
Location: Pemberville, Ohio
Posts: 260
Another way is to monitor the pump inlet line with a point sensor switch. If there is liquid then OK to pump.
Look at the E +H Liquiphant FTL20 types of sensors.
  Reply With Quote
Old July 25th, 2014, 09:07 AM   #4
Mickey
Lifetime Supporting Member
United States

Mickey is online now
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,611
I don't think one can say which is better. But I would go with the level switch.

Most tanks will have a low and high for control and a Low-low and High-High for protection. The extra switches provide extra protection if the low does not shut the pump off the low-low will.

Then again a pressure switch closed to the pump would protect against closed or pinched valves.

Your installation will dictate. Maybe you need both.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old July 25th, 2014, 09:10 AM   #5
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 6,270
For protection against running dry the level switch, regardless of type, is probably the better bet. A low pressure (high suction) switch on the suction side of the pump would be used to protect against cavitation. If you have a flooded suction pump with normal piping that is probably not a problem.
  Reply With Quote
Old July 25th, 2014, 10:21 AM   #6
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 6,152
Level switch is the simplest.

There is however another option to consider if level switch installation is challenging. www.loadcontrols.com has a sensor where you place a CT around a motor lead wire and it can detect pump dry run. It also works if someone closes the pump suction valve.
__________________
True craftsmanship is only one more power tool away.

That's the beauty of processors, they don't have emotions they just run code - The PLC Kid.
  Reply With Quote
Old July 25th, 2014, 10:59 AM   #7
nonuke
Member
Portugal

nonuke is offline
 
nonuke's Avatar
 
Join Date: Sep 2005
Location:
Posts: 840
If you use a level switch, you probably also need a pressure switch because you might have a closed valve after the pump (liquid but no flow). If you use a flow switch you donīt need any other switch.
  Reply With Quote
Old December 12th, 2014, 05:07 AM   #8
Charbel
Member
Lebanon

Charbel is offline
 
Join Date: Jan 2012
Location: Beirut
Posts: 307
Dear,

I assume a flow switch will needs to be located after the pump, because a flap type flow switch before the pump will not make a difference but on the contrary it will stop the pump from running because the pump will need to run to make flow and to make the flow switch work.
I might use a thermal based switch on the discharge but am i not being too late to stop the pump?, the thermal based switch will have to detect no flow in order to stop the pump which is too late?

I think the best would be pressure switch on suction combined with low level switch on the upstream tank

Any thought about this?

Thank you!

charbel
  Reply With Quote
Old December 12th, 2014, 08:39 AM   #9
realolman
Member
United States

realolman is offline
 
Join Date: Mar 2009
Location: here
Posts: 584
I don't think I'd bother with the pressure switch at all

I think it would be more trouble than it would be worth

The flow switch can be a pain as well, and you will have to ignore it till you get the pump started

use floats
  Reply With Quote
Old December 12th, 2014, 09:38 AM   #10
Rumiat
Member
Pakistan

Rumiat is offline
 
Join Date: Dec 2014
Location: Lah
Posts: 2
Well it all depends on your system actually.

If you have a foot valve installed (assuming tank is lower than pump) that would make sure your pump remains primed, just go for a low level switch.

If you choose to use a flow switch, I think you may have to bypass the flow safety system during pump starting and adjusting its suction/discharge valves. So low level is a good option I would say.

Hope this helps.
  Reply With Quote
Old December 12th, 2014, 10:19 AM   #11
nonuke
Member
Portugal

nonuke is offline
 
nonuke's Avatar
 
Join Date: Sep 2005
Location:
Posts: 840
I also use a level limit switch model Liquiphant FTL20 (vibrating forks type) before the pump. If pipe empty, the pump won't run. Works all the time.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Control based on level and VSD Charbel LIVE PLC Questions And Answers 2 March 4th, 2014 11:24 AM
PID ??? Tank level switch feed by a variable valve. ViperDaSnake LIVE PLC Questions And Answers 19 June 26th, 2010 11:16 AM
RS5000 PID Instruction Assistance knight1fox3 LIVE PLC Questions And Answers 27 June 10th, 2010 05:41 PM
Pressure Switch Woes JBradley LIVE PLC Questions And Answers 24 November 7th, 2007 01:42 AM
Lift problem Ladyscarlet99 LIVE PLC Questions And Answers 12 February 16th, 2004 11:39 AM


All times are GMT -4. The time now is 03:00 PM.


.