level switch vs pressure switch
Dear,
For protecting the pump against dry running, it is better to use low level switch in the tank or pressure switch on the suction side? I tend to go for low level switch in the tank to protect the pump from dry run, please advise of any thought. thank you! charbel |
![]() |
![]() |
#2 |
Member
|
Why not use a flow switch after the pump of the type: IFM - SI5000
|
![]() |
![]() |
#3 |
Member
|
Another way is to monitor the pump inlet line with a point sensor switch. If there is liquid then OK to pump.
Look at the E +H Liquiphant FTL20 types of sensors. |
![]() |
![]() |
#4 |
Lifetime Supporting Member
|
I don't think one can say which is better. But I would go with the level switch.
Most tanks will have a low and high for control and a Low-low and High-High for protection. The extra switches provide extra protection if the low does not shut the pump off the low-low will. Then again a pressure switch closed to the pump would protect against closed or pinched valves. Your installation will dictate. Maybe you need both.
__________________
Mickey If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else. ----- Chinese Proverb |
![]() |
![]() |
#5 |
Lifetime Supporting Member
|
For protection against running dry the level switch, regardless of type, is probably the better bet. A low pressure (high suction) switch on the suction side of the pump would be used to protect against cavitation. If you have a flooded suction pump with normal piping that is probably not a problem.
|
![]() |
![]() |
#6 |
Lifetime Supporting Member
|
Level switch is the simplest.
There is however another option to consider if level switch installation is challenging. www.loadcontrols.com has a sensor where you place a CT around a motor lead wire and it can detect pump dry run. It also works if someone closes the pump suction valve.
__________________
True craftsmanship is only one more power tool away. That's the beauty of processors, they don't have emotions they just run code - The PLC Kid. |
![]() |
![]() |
#7 |
Member
|
If you use a level switch, you probably also need a pressure switch because you might have a closed valve after the pump (liquid but no flow). If you use a flow switch you donīt need any other switch.
|
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Jan 2012
Location: Beirut
Posts: 307
|
Dear,
I assume a flow switch will needs to be located after the pump, because a flap type flow switch before the pump will not make a difference but on the contrary it will stop the pump from running because the pump will need to run to make flow and to make the flow switch work. I might use a thermal based switch on the discharge but am i not being too late to stop the pump?, the thermal based switch will have to detect no flow in order to stop the pump which is too late? I think the best would be pressure switch on suction combined with low level switch on the upstream tank Any thought about this? Thank you! charbel |
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Mar 2009
Location: here
Posts: 584
|
I don't think I'd bother with the pressure switch at all
I think it would be more trouble than it would be worth The flow switch can be a pain as well, and you will have to ignore it till you get the pump started use floats |
![]() |
![]() |
#10 |
Member
![]() ![]() Join Date: Dec 2014
Location: Lah
Posts: 2
|
Well it all depends on your system actually.
If you have a foot valve installed (assuming tank is lower than pump) that would make sure your pump remains primed, just go for a low level switch. If you choose to use a flow switch, I think you may have to bypass the flow safety system during pump starting and adjusting its suction/discharge valves. So low level is a good option I would say. Hope this helps. |
![]() |
![]() |
#11 |
Member
|
I also use a level limit switch model Liquiphant FTL20 (vibrating forks type) before the pump. If pipe empty, the pump won't run. Works all the time.
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Control based on level and VSD | Charbel | LIVE PLC Questions And Answers | 2 | March 4th, 2014 11:24 AM |
PID ??? Tank level switch feed by a variable valve. | ViperDaSnake | LIVE PLC Questions And Answers | 19 | June 26th, 2010 11:16 AM |
RS5000 PID Instruction Assistance | knight1fox3 | LIVE PLC Questions And Answers | 27 | June 10th, 2010 05:41 PM |
Pressure Switch Woes | JBradley | LIVE PLC Questions And Answers | 24 | November 7th, 2007 01:42 AM |
Lift problem | Ladyscarlet99 | LIVE PLC Questions And Answers | 12 | February 16th, 2004 11:39 AM |