COMMUNICATION LINL B/W MODICON & S7 300 PLC

shabi

Member
Join Date
Nov 2005
Location
Dubai
Posts
9
Hi , i have one task i have to stablished communication link b/w modicon & S7 300 Plc over Ethernet TCP/IP protocol. connection medium b/w them is Fiber optic i am using SCALANCE X 204-2 to convert Fiber optics in Ethernet TCP/ip protocol. can any body send me the connection diagrams
 
You should check with your PLC suppliers. The native Ethernet for Modicon is Modbus/TCP and the native Ethernet for Siemens is Profinet - essentially Profibus over Ethernet. I'm not sure they have directly compatible protocols. You may need a communications bridge.
 
You can use 343-1 communication processor in S7-300 or S7-300's with integrated Ethernet interface and write your own program to communicate via Modbus TCP protocol. I've tested it with some of applications using my own Modbus TCP Master code for S7 PLC's.
 
Last edited:

Similar Topics

Hello We have installed several G.E. Fanuc 90 70 PLC Everything was ok but suddenly we can not communicate anymore with any PLC with the software...
Replies
0
Views
33
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
51
Hi all I need help on this As in my project used Schneider TM241 controller. Now I want to communicate Elite energy meter with controller by...
Replies
3
Views
117
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
Replies
4
Views
84
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
Replies
1
Views
90
Back
Top Bottom