Stuck, Confused Help needed!!!

RogerBrunner

Member
Join Date
Feb 2017
Location
Florida
Posts
42
I am using IDEC Smart Relays with WIndGLC software with Function block programming.

I1,9,12, and 13 are all momentary triggers, I need to slip in I13 with additional functionality. 13 needs to delay the Q from activating for 6 seconds.

My issues they are all momentary any help would be great.

PLC.JPG
 
Does the Q for I13 stay on or is pulsed?
You could use a RS block with I13 connected to SET, then have the RS block drive a TON timer, the output of the time drives the Q. The question is what RESETS the RS Block.
 
Add an Offdelay timer to i13. The output of this timer should be inverted and linked using AnD with whatever drives the Q....

This idec smartrelay is a labelled logo controller from siemens. Lots of tips and tricks on the siemens logo microsite.
 

Similar Topics

Hi, I am using M221 reading from 3 different sensors (modbus rs485) sharing same bus (daisy chain). I am currently using READ_VAR (in total...
Replies
0
Views
67
I'm using one TON (called SystemTimer) throughout a program that I change the .PRE given different conditions. I'm porting an IDEC ladder over to...
Replies
8
Views
257
We have a keg check weigher that that lost a fight to a forklift. The scale was previously a Systec IT3000, which was the only PROFIBUS slave...
Replies
5
Views
646
really strange issue. The panelview(2711p-T10C22D9P) will try to load an application and get stuck on "Starting Alarms". If I reboot the...
Replies
4
Views
1,328
Have an issue with a couple of KTP700F HMI's that gets stuck on the startup in the Windows screen and not loading the HMI project. THis is not the...
Replies
3
Views
1,314
Back
Top Bottom