hello,

I am trying to connect the analog proportional regulator from Festo (VPPM-6L-L-1-G18-0L6H-A4P-S1) to automation direct analog output module F2-4DA2AD which is a current sinking module.

festo didn't specify if the input signal supposed to a sink or source signal. i have attached both the output module and valve wiring diagram.

can some one help me with this ?

appreciate the help!

output_module.PNG valve.PNG
 
I'm not too familiar with the Automation direct PLC but if I was going to connect then the bottom leg (+) would go to the + of the 4-20 signal of the valve and the -v would go to the card output (top leg). Do not ground either leg only the screen of the cable, if you look at the analogue input it is configured the same way but is marked up as + bottom leg, providing the potential is correct way round then it should work ok, I have seen many people wire sensors of many types in the wrong way round and as far as I can remember this has never caused any damage.
 
The Festo analog input just wants to see a current signal. It doesn't know whether the current is provided from an active (sourcing) or a passive (sinking) analog output.

But the Automation Direct Analog Output is a passive/sinking analog output that requires a DC power supply (p/s, typically 24Vdc) to provide power to the output loop.

DC p/s (+) wires to Festo (+) Terminal 4

Festo (-) terminal 3 wires to the A-D OUT1+ or the A-D OUT2+ terminal, depending on which analog output is to be used.

DC p/s (-) wires to A-D 0VDC terminal (at the top)

The Festo's DC power supply has to be at the same ground potential as the A-D because the A-D module is single ended/common grounded.
 
Before wiring the system as stated i would check to make sure pin 3 and pin 7 on the Festo are not common to each other. I'm not fully convinced that the input is isolated. At least the Festo document I looked at doesn't directly state that it is.

Keith
 
thanks everyone who responded. appreciate it.

I wired exactly as danw mentioned, i did not check the current output from the module but valve did not respond and i can see there is 25 % of full scale in the PLC program.

I was using a voltage (0-10V) proportional controller before with the converter in the middle which is working, i used this to test the loop current flow.

operating manual says that it is a differential input set point to the valve, correct me if i am wrong but in this case we need to connect - Ve of the setpoint which is 3 to the 0V of the DC p/s right ?

I will check that kamenges, probably it is.
 
The differential input thing would apply more to voltage than to current. But if they maintained the design philosophy between the voltage and current input models then the current input should be isolated. This would mean that 3 IS NOT internally connected to 7 and that danw's connection description is correct.

Do you have an independent way to determine if the correct current is being delivered from the output module, like a meter?

Keith
 

Similar Topics

Hi, I am an inventor looking for a way to automate a block-making press I made out of a log splitter. It makes blocks for building homes from...
Replies
11
Views
7,176
VALVE MODEL # 4WRPEH 6 C3 B04P-20/G24K0/A1M VALVE MODEL #...
Replies
6
Views
5,911
Hi to everyone. As a part of my project I have an analog input. I looked for FC105 and the control of analog signals. The quality of air is being...
Replies
43
Views
7,489
Have a question about controlling a 4-20ma steam valve by the use of a temperature process controller instead of a plc. This is something that we...
Replies
8
Views
6,374
Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
Replies
1
Views
61
Back
Top Bottom