Issue with wizard for powerflex 525 in studio 5000

jakeparsons03

Member
Join Date
Jun 2017
Location
Indiana
Posts
78
Hey all,

I am having an issue when I get to the direction test of a powerflex 525. It says there is a communication issue. But I can change all parameters still. When I go to tuning it gives another error.

"There was an unhandled exception....object of type RADrvAPI.StatusFeedbackEventArgs cannot be converted to RADrvAPI.LostControlEventArgs"

Has anyone seen this?

Thanks in advance!
 
Not this specific issue, but I've had problems when the logic is trying to control the drive at the same time as doing a test or autotune.
 
Not this specific issue, but I've had problems when the logic is trying to control the drive at the same time as doing a test or autotune.

I was taught to always change the start control to the keypad and disconnect the Ethernet for Auto tuning.

Right or wrong, it works for me 100% of the time. Just make sure the Ethernet loos parameter isn't set to fault.
 

Similar Topics

It's been a while since I've done a Powerflex w/o a hardwired enable (enabling over Ethernet/IP). So I'm struggling with how you are run the...
Replies
2
Views
1,388
I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
Replies
14
Views
176
Hi everyone, I have an issue with installation of Studio 5000 33.00.02 DVD Media disc 2 with View Designer on Windows 11. After installation...
Replies
0
Views
68
Hi Folks, I am in the process of retrofitting MRJ2 (Mitsubishi) series with MRJ4 servo drives for two axes. I did use the conversion kit...
Replies
3
Views
77
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
5
Views
224
Back
Top Bottom