Modbus RTU Issues
Apr 2017
Watertown
Hi Everyone,
I seem to be having issues communicating through Modbus RTU from my Horner XL7e to my Emerson Drives. The Connection is there but the drives are supper slow to respond.
Seems to me like a conflict somewhere but, I can not seem to find what's holding me up. At first I thought it was a bad port on the PLC because I stole a PLC that runs the same program from a currently running machine and everything works fine. So I ordered a new touchscreen and the same thing is happening SLOW responses from the drives.
any help or suggestions would be greatly appreciated.
https://accautomation.ca/horner-xl4-modbus-rtu-instructions/
The above thread will show the XL4 communicating to a Solo process controller via Modbus RTU (RS485)
A couple of things to check.
- RS485 termination resistor
- Ensure all of the parameters like parity, bit rate, stop bits are the same on all of the devices.
- Increase the baud rate to see if speeds improve.
On the Horner a status register can be programmed into the communications. Does it contain any information?
Just a couple of thoughts.
Regards,
For speed considerations, I map my registers into Menu 0. I usually have 0.060 through 0.063 for my writes (to the drive), and 0.064 to 0.070 for my reads (to the plc).
Also, are you using the CT RTU driver? It's on the Horner web site. Seems to work better than the generic Modbus.
Gene Bond,
Where is this CT RTU Driver located on there site? I use there site quite often and can not seem to find it.
I also don't quite understand what you are saying here "I map my registers into Menu 0. I usually have 0.060 through 0.063 for my writes (to the drive), and 0.064 to 0.070 for my reads (to the plc)." can you explain a little more on this.
OK, I was referring to the SK, SP, Unidrive M series (General Purpose through High Performance Drives). The Epsilon series is Servo Only.
The CT-RTU protocol is still appropriate, though. I believe it was developed for the Epsilon series, but works well on the general purpose drives as well.
Also note that Control Techniques is no longer an Emerson Brand. Emerson sold CT to Nidec about 2 years ago...
Gene Bond,
So if i do the conversion from Mod bus to CT RTU is there anything i have to adjust or is it a straight forward thing. I have never worked with CT RTU before so unsure.
Should be straight forward. The addresses are the same.
If you want to see a different picture of what addresses are what, you may want to play with a project in CTvue Configurator 3
Remember that the Modbus address can be +/- 1 digit... I don't recall which is what, but I seem to remember that CTvue is -1 from the menu address.
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
217
I am using a 1769-L35e with a 1769-SM2 (latest firmware) to communicate with a MicroMotion transmitter (9739MDV) that automatically detects serial...
3,554
Ok, so I have been wading through endless amounts of threads on this issue and I am still having no luck resolving my issue. I am trying to us a...
25
5,406
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
46
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
250