Totalizing volume with a level transmitter

Is this reasonable to do?

I am using a SLC 5/05 so there's no totalizing instruction, I think I have to make my own. Anybody done this, any starting points to consider?

To make it even more fun, the receiver tank may or may not be emptied during the cycle, and may or may not have leftover from a previous cycle.
  Reply With Quote
Old September 16th, 2020, 05:25 PM   #2
Ken Moore
Lifetime Supporting Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: North, West, South Carolina
Posts: 2,847
Usually totalizers are used with flow meters. Is that what you have?

Using a level transmitter, you should be able to calculate the volume based on the current level. You will need the tank dimensions and a little math.
__________________
https://azr.com/
  Reply With Quote
Old September 16th, 2020, 05:26 PM   #3
Lare
Member
Finland

Lare is offline
 
Join Date: Jan 2006
Location: Finland
Posts: 1,405
Calculated volume change.


It depends if tank is filled before emptying or filled same time than emptying.

Now as it same time emptyed and filled, you need to know both level change and output flow to outside from tank same time. (Volume = flow out + level change * tank bottom area)

If both filling and pumping out is same speed, level never changes and it makes everything more fun.






Is emptying allways with same flow or is flow changing all time?

(If speed / flow is constant, you can forgot level change and calculate only pumping time (s) * flow litres / s = volume

Last edited by Lare; September 16th, 2020 at 05:35 PM.
  Reply With Quote
Old September 16th, 2020, 05:36 PM   #4
Robb B
Member
Canada

Robb B is offline
 
Join Date: Feb 2011
Location: canuckistan
Posts: 90
Quote:
Originally Posted by Ken Moore View Post
Usually totalizers are used with flow meters. Is that what you have?

Using a level transmitter, you should be able to calculate the volume based on the current level. You will need the tank dimensions and a little math.
No flow meter, I believe it's a magtech level transmitter. I can get the volume okay, it's how to add it that I'm not sure on. Obviously the ADD instruction, but how can I use the max value before it gets emptied? And then add that to the next quantity, and so on.
  Reply With Quote
Old September 16th, 2020, 05:42 PM   #5
Robb B
Member
Canada

Robb B is offline
 
Join Date: Feb 2011
Location: canuckistan
Posts: 90
Quote:
Originally Posted by Lare View Post
Calculated volume change.


It depends if tank is filled before emptying or filled same time than emptying.

Now as it same time emptyed and filled, you need to know both level change and output flow to outside from tank same time. (Volume = flow out + level change * tank bottom area)

If both filling and pumping out is same speed, level never changes and it makes everything more fun.






Is emptying allways with same flow or is flow changing all time?

(If speed / flow is constant, you can forgot level change and calculate only pumping time (s) * flow litres / s = volume
The source of condensate is from a vacuum cycle, so the flow will be irregular. In addition it may be repeated several times until no more condensate accumulates. I will be adding an input signal to the PLC for when the tank is drained by a valve.
  Reply With Quote
Old September 16th, 2020, 05:50 PM   #6
Lare
Member
Finland

Lare is offline
 
Join Date: Jan 2006
Location: Finland
Posts: 1,405
Check P.M
  Reply With Quote
Old September 17th, 2020, 03:17 PM   #7
Robb B
Member
Canada

Robb B is offline
 
Join Date: Feb 2011
Location: canuckistan
Posts: 90
Well I think I have an in-progress solution. I think it is simpler than I was considering. For whatever reason I can't add pictures from this location (IT issue I think) but basically it's just moving the calculated volume to a register, then adding the moved volumes each time the tank is drained (can't add to the tank while draining, since it's part of a vacuum circuit). Then I just have to program it to deal with operator errors...
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
level transmitter shkoko2000 LIVE PLC Questions And Answers 3 May 31st, 2016 11:26 AM
reducing waving readings on a Level transmitter. buhnen LIVE PLC Questions And Answers 8 April 17th, 2009 04:47 PM
Bubbler method to measure solution height in tanks manmeetvirdi LIVE PLC Questions And Answers 13 November 23rd, 2007 12:20 PM
Lift problem Ladyscarlet99 LIVE PLC Questions And Answers 12 February 16th, 2004 11:39 AM
Counter Question Kunjal LIVE PLC Questions And Answers 3 November 30th, 2002 11:14 AM


All times are GMT -4. The time now is 04:44 PM.


.