PVPlus Compact 600 mer error

Hello Everyone,

I have created project in FTview 8.0 (ME edition). Now trying to transfer application to HMI PvPlus Compact 600. But when I create runtime application, I get following error message.
This error is coming only for compact HMI edition. I have attached error file. I am unable to attach ".apa" as file size is more than 1mb, but if possible please download it from following link and plz tell me where I am going wrong. Backup is very primary.



Please guide me through this.



Thanks,
Shailesh
Attached Files
File Type: txt cHECK_NEWValidationResults.txt (1.5 KB, 14 views)
  Reply With Quote
Old April 27th, 2016, 12:44 AM   #2
shailesh_vb
Member
India

shailesh_vb is offline
 
Join Date: Jun 2013
Location: Pune
Posts: 41
Hello Everyone,

Sorry, my backup link is as below:-

https://www.sendspace.com/file/p277j8

Please guide me through this.



Thanks,
Shailesh
  Reply With Quote
Old April 27th, 2016, 12:49 AM   #3
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 3,125
The problem is right there in your text file...
Quote:
Only the Ethernet, Serial DF1 and Serial DH485 drivers are supported by Compact Machine Edition applications.
You have a communication driver configured that is not supported on a PanelView Plus Compact. Check out your Communication setup.
  Reply With Quote
Old April 27th, 2016, 01:06 AM   #4
shailesh_vb
Member
India

shailesh_vb is offline
 
Join Date: Jun 2013
Location: Pune
Posts: 41
I have attached link backup link in above thread. I have used ethernet driver for communication and I am able communicate on PC when I test application.

I did't find driver named "RsLinx Classic" or "Micro850" in communication setup. I have attached sscreeshots for details. Please go through it.


Thanks,
Shailesh
Attached Images
File Type: jpg Communication setup.jpg (43.8 KB, 8 views)
File Type: jpg Tag Browser.jpg (57.3 KB, 7 views)
  Reply With Quote
Old April 27th, 2016, 10:00 AM   #5
shailesh_vb
Member
India

shailesh_vb is offline
 
Join Date: Jun 2013
Location: Pune
Posts: 41
Hello Guys,

Any guess on above query??



Shailesh
  Reply With Quote
Old April 27th, 2016, 10:21 AM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 15,559
FactoryTalk View thinks you have mis-named or mis-configured drivers. If you have RSLinx Classic defined in the project tree as a data server, remove it.

Look on the "Runtime/Target" tab to see if you there are drivers there that were previously created during experimentation or development.

To copy the Development driver schema (which you have stated works correctly) to the Target tab, click that big "Copy from Design to Runtime" button.
  Reply With Quote
Old April 27th, 2016, 11:28 AM   #7
shailesh_vb
Member
India

shailesh_vb is offline
 
Join Date: Jun 2013
Location: Pune
Posts: 41
Hello Ken Roach,



Worked.
You are the saviour.

One more question, I want to move value into one of the Integer. But don't know how to write expression for it??



Thanks,
Shailesh

Last edited by shailesh_vb; April 27th, 2016 at 11:36 AM.
  Reply With Quote
Old April 27th, 2016, 02:40 PM   #8
shailesh_vb
Member
India

shailesh_vb is offline
 
Join Date: Jun 2013
Location: Pune
Posts: 41
i want to do above function in hmi..
  Reply With Quote
Old April 27th, 2016, 05:07 PM   #9
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 15,559
Quote:
I want to move value into one of the Integer.
My guess is that you want to type a value in on the screen and have that value written to the PLC controller.

In general, this is done with a Numeric Cursor Input Point object.

Can you describe in more detail what you mean by "move value into [an] Integer [tag in the controller]" ?
  Reply With Quote
Old December 10th, 2019, 11:00 AM   #10
jotamann
Member
Spain

jotamann is offline
 
Join Date: Nov 2019
Location: At work
Posts: 1
Hello everyone

I've had the same trouble trying to create the runtime for a PanelView Plus 600 Compact.

The point is the FactoryTalk's comms driver (FactoryTalkLinx or RSLinxEnterprise) is detecting there is a not supported driver in the shortcut configuration. Specifically it's named RSLinxServer.

The solution has been:
1. Delete all drivers configured in RSLinx
2. Close RSLinx
3. Kill every RSLinx processes from Windows Task Manager
4. At the shortcut configuration in FactoryTalkLinx/RSLinxEnterprise:
4.1 Expand the first backplane and delete "RSLinx Server" node at Design tab.
4.2 Do the same for the Target tab: delete the node "RSLinx Server" located in the first backplane.
5. Add the shortcuts manually, verify and accept them.
6. Create again the runtime.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Panel view plus compact 600 does not working on runtime suvro2012 LIVE PLC Questions And Answers 2 April 19th, 2015 01:33 PM
612 error code at PV 600 Abo Hozifa LIVE PLC Questions And Answers 13 March 31st, 2015 05:53 AM
No upload from panelview plus 600 compact memberpeace LIVE PLC Questions And Answers 3 January 26th, 2011 01:00 PM
Compact logix and panel view plus 600 compatibility issue ALT LIVE PLC Questions And Answers 18 December 25th, 2010 06:36 AM
MPI comunication Manuel Raposo LIVE PLC Questions And Answers 22 July 16th, 2007 07:24 AM


All times are GMT -4. The time now is 05:38 AM.


.