I am using a PLC to read some Modbus addresses from a Yokogawa GM10 data recorder. The addresses are 302001-302010, and also 415001-415010?

I thought addresses had to be no more than 65,535.

Is address 302001 the same as 2001???

What about address 415001?

Thanks.

FNC
 
Some software uses 400000 insteaf of 40000 (they all have an Extra 0.

I am not sure why exactly, im hoping someone else can enlighten me on this,

But for 302001, it would be 32001, etc.

Im just not sure on the 415001.
It is very possible that it talks enron modbus, and Function code 3 (read analog inputs), register 2001 and function code 4 (read holding registers), register 15001...
 
telling more about the plc and soft used could help because it would be different from one to another.
Some will decide of the first number by using a function code and then you just type the other numbers.
 
Modbus addressing is notoriously confusing to novices because the prefix digit describes the data table type, not the "10 thousands place" offset.

0 Discrete Output Coils
1 Discrete Input Contacts
2 not used
3 Analog Input Registers
4 Analog Output (Holding) Registers

Most users will number the first Holding register as "40001", even though the Function Code to read it is 0x03 and the Offset is 0x00.

Some vendors add another zero, some consider the first register to be 0 instead of 1... it gets weird.

Page 332 of this user manual gives some interesting information:

https://web-material3.yokogawa.com/IM04L55B01-01EN_012.pdf


The data from "sub unit 2" is considered Yokogawa "Channel 2001 data", which is represented as Modbus register 315001.


My quick reading of that manual suggests that the same data can be read as a "Analog Input" or as an "Analog Output / Holding" register, so as a 3000x address or as a 4000x address.
 

Similar Topics

Hello guys, I used modscan32 before to read data using TCPIP based on given IP Address, Device ID and etc. The data I used to read in modscan32...
Replies
19
Views
3,655
Hello, i have a curios problem in a modbus tcp reading from a client. The HC900's answer for the variable 20 (holding register 6375) is clear in...
Replies
17
Views
3,077
Hi, I have been struggling for a week with FATEK FBs-24-MAR-AC PLC. My goal is to read voltage and current from a powermeter Elnet Pico 5. The...
Replies
8
Views
3,649
Hi all, Has any of you got any example of reading data from modbus tcp, using FBD? I am just trying to get my head around, doesnt look like a...
Replies
6
Views
2,483
Hey guys, I'm working on an existing system for a client where a GE RX3i at a tank/pump station is sending data to their office HMI through a...
Replies
1
Views
3,810
Back
Top Bottom