Slc504 To Dh485 Panelview

BENNY

Member
Join Date
Mar 2003
Posts
22
I have an existing DH+ network and I would like to add a DH485 panelview (2711-K5A2)to an SLC-504. I know that channel 0 needs to be configured for DH485, but I'm confused as to what cables or adapters I need to connect the panelview to the slc. The panelview will only be communicating to this slc. I did do a search on this forum and the ab website, but I'm still uncertain as to what hardware is required. Thanks in advance for any help.
 
Then connect a 1747-PIC to the serial port (Channel 0) of the 5/04. Then a patch cable (such as a 1747-C10) from the PIC to a 1747-AIC module. Then another similar patch cable to the DH485 connector on the PanelView terminal.

So the hardware you will need will be:

(1) 1747-PIC
(1) 1747-AIC
(2) patch cables (1747-C10 or similar)

That should do the trick. I just set that up with some spare equipment and they are able to see each other just fine.

And of course as you mentioned, Channel 0 needs to be configured for DH485.

OG

edit: one last thing, the AIC has to be powered (24V dc).
 
I would check into the 1761-NET-AIC (AIC+). It is an RS-232(DH-485) to DH-485 converter.

[attachment]

In a simple 2 node application like this, I don't think a second AIC+ is necessary for the Panelview.

I'll do some digging and find the part numbers for the cables...

dh485.gif
 

Similar Topics

1747-L541 processor. I was given a program to load into this PLC. When downloading via DF1 there's a message that the communication will be lost...
Replies
5
Views
797
I am having an odd issue. After upgrading to FTView-10.01; I can no longer see tags on a microlgix1100 and a SLC5/04 that is going through a...
Replies
8
Views
3,447
I'm looking for a cheap way to pull data from a controllogix system to a SLC504 so that I can use the DH+ connecting on the 504 which is connected...
Replies
3
Views
2,319
Thanks for the replies following my initial post Re connecting via serial to a DH485 PV1000 We have now found a 1761-NET-AIC and a 1761-CBL-AS03...
Replies
0
Views
1,709
Back
Top Bottom