AB PLC communication to Drive and SCADA
randheerp
Aug 2006
Bangalore
77
I have an AB PLC with an Ethernet Port (L32E). If I want to communicate with 3 drives and a SCADA,
1. How I can connect it?
2. Is it a workable solution if I connect 3 Drives and a SCADA to PLC through a Ethernet Switch with different protocol for SCADA and Drives?
Or, its workable solution only if PLC Communication to 3 Drives and SCADA is through the same PROTOCOL (eg:Modbus)?
3. Or we can't connect Drives and SCADA to the same network?
The CompactLogix controllers support both cyclic (for I/O and control) and explicit (for monitoring and editing) data transfer over EtherNet/IP protocol through the same Ethernet port.
In general you can run both functions of the EtherNet/IP protocol on the same Ethernet network.
The CompactLogix does not support Modbus/TCP via its Ethernet port. You would need a Prosoft MVI69-MNET module or some other converter to run Modbus/TCP.
Hello friends. Pliz help me with communication. We have PLC Fatek FBs-20MC and Rexroth DKC02.3. What message should I send to Rexroth to...
1,342
Dear Sir, I have a healthy profibus communication between SIEMENS PLC S7 400 and Allen Bradley drive PF700 using 20-comm-p profibus dp module...
2,807
hello guys... I have done communication with omron cp1l plc and yasakawa v1000 ac drive now I'm able to write drive parameter from plc program...
3,063
Hello Experts, I have Siemens 315-2PN/DP and drive from third party. Drive is sitting on Profinet network and it is working fine. Now the customer...
2,353
I do programming in GX developper for ABB drive model ACS 550 control via modbus communication in FXCPU PLC,I can read the Data of drive...
3,165