Using EDS file to configure message

I`m trying to command a Mitsubishi inverter F800 using a Micrologix PLC with message instructions.

I sucessfully controled it using a Compact Logix with a EDS file.

Opening the EDS file i have these information:


[Params]
Param1 =
0, $ reserved, shall equal 0
6,"20 29 24 01 30 03", $ Link Path Size, Link Path
0x0000, $ Descriptor
0xC1, $ Data Type
1, $ Data Size in bytes
"Run forward", $ name
"", $ units
"Run forward", $ help string
0,1,0, $ min, max, default data values
,,,, $ mult, div, base, offset scaling
,,,, $ mult, div, base, offset links
0; $ decimal places

Is possible to decode the "link path" to send information using message or another instruction ?
  Reply With Quote
Old September 16th, 2016, 01:42 PM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,679
Welcome to the Forum !

When you say you "controlled" the F800 with the CompactLogix, do you mean you put it into the I/O tree and used the cyclic I/O connection ?

While it's possible to send CIP Generic messages using the MicroLogix 1100 or 1400 controllers, it is likewise very strongly recommended AGAINST to use that method to control a variable-frequency drive.

The MicroLogix simply isn't designed or built to do control over an Ethernet network. It doesn't have the cyclic I/O connection capability or a dedicated daughtercard to handle those functions.

If you're going to do the stop/start control over hardwire and use messaging to retrieve status data or occasionally send a configuration parameter, my stance softens somewhat.
  Reply With Quote
Old September 16th, 2016, 03:01 PM   #3
Fr-Felipe
Member
Brazil

Fr-Felipe is offline
 
Join Date: Sep 2016
Location: SC
Posts: 2
Hi Ken, thank you for the warm wellcome !

Exactly, i controled the F800 with cyclic I/O connection.

And stop/start will be controled using hardwire, but i need to change speed occassionally.

I can read and write parameters to the inverter, but i can't change the frequency sucessfully, in that point enters the EDS file, i want to look where this value is being written.
  Reply With Quote
Old September 16th, 2016, 04:06 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,679
You are correct that the EDS file provides clues to the DeviceNet module objects supported by the device.

Can you post a link to the EDS file you are using for this drive ? I could not find one with a brief search of the Mitsubishi website.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Registering an EDS file Steve Bailey LIVE PLC Questions And Answers 13 March 21st, 2017 02:16 PM
EDS File Error ccaltagi LIVE PLC Questions And Answers 3 October 5th, 2011 07:15 PM
EDS file for ethernet communication jcp LIVE PLC Questions And Answers 2 January 28th, 2011 01:52 AM
RSNetwrx CntrlNet eds file not registered jetuaime81 LIVE PLC Questions And Answers 6 January 16th, 2009 10:04 AM
EDS File for 1794-ACNR15 FLEX I/O ControlNet Adapter (Redundant Media) shiftedbits LIVE PLC Questions And Answers 2 May 10th, 2007 01:14 PM


All times are GMT -5. The time now is 11:37 PM.


.