Rate display on Red Lion PAXLCR00

irondesk40

Member
Join Date
Jan 2008
Location
nc
Posts
630
Looking at using a Red Lion for rate display and confused on the instructions for programming.
Max speed = 7730 RPM
Distance Per RPM = 10.6 inches
Encoder pulses per rev = 100
Total revs to equal 1 foot = 1.132
Total pulses per foot = 113.2

Parameter values to show feet per minute
RT- DISP = 60
RT-INP = 113.2
LO-UDT = 01.0
HI-UDT = 02.0

If i understand it correctly this is the only parameters you would enter. If anyone has used these, could you verify if i understand it correctly.
Thanks
 