Problem with S7414 using S5 I/O

AD77

Member
Join Date
Feb 2010
Location
Southern England
Posts
11
I've got a problem with an S7 414-3 PN/DP talking to S5 I/O in a 185U rack via a IM 463-2 and IM314.

Basically the problem is that the S7 IM is happy with the S5 rack (it can see it and when I change parameters on the IM314 you get the errors on the S7 etc.) but it doesn't see any changes in the S5 inputs and won't put on any of the outputs.

I have tried two different IM 314 cards and two different cables, different I/O cards, different addresses and I'm now starting to run out of ideas.

We've proved the S5 rack with an S5 processor. So it's got to be either a failed IM 463 or something in the S7 config that's wrong (or I've been really unlucky with 2 IM 314 cards or 2 cables).

We're currently using a very simple S7 project, just the processor and IM card in the HW with one range of addresses and one input card in the S5 rack.

Has anyone got any suggestions?
 

Similar Topics

The project on the operator workstation keeps disconnecting, even though I have an installation server and operating station set up through...
Replies
0
Views
51
I have a problem, I'm running an AE Licence Manager on a Windows 2016 Server, and my Window Maker is on another separate Windows 2016 Server. My...
Replies
0
Views
71
I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
Replies
1
Views
78
Hello, I need to write the following program in Ladder language, but I could not integrate the Fibonacci sequence into the ladder. Can you help...
Replies
22
Views
529
On all pages of my project i have a lot of information, texts and details that should not not be shown. I can remove them for each part apart from...
Replies
0
Views
70
Back
Top Bottom