Error at panel view 1000 at start p.
AB2005
Nov 2006
Lahore
318
Dear Friends;
We have Allen Bradley Panel View “Panel View plus 1000” with Compact Logic PLC. I faced a problem with panel view that it had two program files in its “Internal” memory name “530557p1_Jb.mer” and “530557p0_Jb.mer” and the first one was operational (there was no memory card). I wanted to run the second file (finally), so I deleted the first file (530557p1_Jb.mer), loaded the second one (530557p0_Jb.mer) and run the project. Every thing was ok but when I cycled the power, the panel view displayed an error (picture attached) that system could not found the file 530557p1_Jb.mer while it was deleted and the other one loaded. I could understand the problem so I renamed the second file “530557p0_Jb.mer” as ‘530557p1_Jb.mer’, run the project and found no error appeared after cycle the power.
I want to know what I made mistake that I faced such problem and how to prevent it occurring again.
I have not got a panelview in front of me, but I think there is an option where you can select which file loads when the panelview first starts.
Because you deleted that file that was specified, the panelview couldn't find it, hence the message you got.
I'll be back in the office tomorrow so I can check where the setting is.
Mark
the bad news is, don't delete or rename anything with out a backup.
you have deleted the running file
attempt to rename your file back to it's own original name
Choose the file manager load that file then run that file
You might be lucky
As others mentioned, if you delete or rename an application that was selected to run at startup, you get this message.
I would first load the application that you want to load at startup, then go to Terminal Settings > Startup Options > ME Station Startup. Toggle to "Go to Configuration Mode", then back onto "Run Current Application". This will set your application that is currently loaded to run at startup.
Dear dmroeder;
Thank you very much. I got your point and checked, my problem solved but this is not a legal way to solve the problem. Is there no any way to remove this error?
Hello, I was wondering if any of you have came across this issue I am having. I can download to a 12" IC754VSI2CTD-KJ with my old Windows 7 laptop...
1,929
Hi I have a problem described below: I have a panelview application which is actually running on a 2711R-T4T panelview 800 which I call the "old"...
3,528
Hi Friends, I'm getting several same error messages; ''Timed out Reading F28:9 from MircoLogix at 192. 168.0 30'' from a Panel View Plus 700...
2,020
I am trying to hook up a GE QuickPanel View to an Allen Bradley MicroLogix 1000 via serial. Once I load the runtime into the View I get the...
4,492
Hello guys, im in big trouble, a few days ago turning up a machine we came acros this screen, its a Panel View 600 btw. Checking the...
4,890