have recieved from machines from germany that have 2 seperate 24 volt dc power suppplies. They have one that used for the plc inputs,outputs etc. and then there is another that is used on the analog input and high speed counter input cards.
Is this a good pratice. From the schematics the DC common of each power supply are not connected.
The reason i ask is that we have had these machines for about a year and experienced multiple failure of the some of the flow meters that are powered off the one power supply used for the analog and counter cards. Basically what they did was take a 24vac tap on the main transformer and it goes to a circuit board with just 4 diodes and a capactior and that is how they are getting the 24vdc for the analog and counter cards. With AC inverters on these machines and with about 15 of them side by side with a scope you can see a lot of noise and spikes on the 24vdc out this what i consider a cheap power supply.
Is this a good pratice. From the schematics the DC common of each power supply are not connected.
The reason i ask is that we have had these machines for about a year and experienced multiple failure of the some of the flow meters that are powered off the one power supply used for the analog and counter cards. Basically what they did was take a 24vac tap on the main transformer and it goes to a circuit board with just 4 diodes and a capactior and that is how they are getting the 24vdc for the analog and counter cards. With AC inverters on these machines and with about 15 of them side by side with a scope you can see a lot of noise and spikes on the 24vdc out this what i consider a cheap power supply.