Error 701-8004250A.Failed to go online with controller. Unable to Open connection

asim_rana

Member
Join Date
May 2005
Posts
50
Problem Faced:
• We are unable to connect with CPU via Rslogix 5000
• Whenever we try connecting we receive an error “Error 701-8004250A.Failed to go online with controller. Unable to Open connection—All connections may be in use”. Please refer the below image

• Everything was fine till few days ago & we are able to go online.
• Attached is the overall system Topology for your reference.( system Topology.pdf)
• Please refer below the screen shoots taken using Logix5000 task monitor utility. Apparently we have 262 available connections & we are not using more than 40 .Additionally CPU utilization also seems reasonable around 13 %,

Controlnet CPU usage is 100 %

• Furthermore when we browse Rslinx, we cannot see the secondary CPU. Please refer the below image

• When we are trying to upload from RSnetworx, we cannot see secondary CPU & the error code CNET:8222 is appearing. Please refer the attached snapshots

• System Overhead slice time is currently at 20%
NUT is 5msec & RPI is 40msec
• We are able to receive data in DCS & all IOs are also OK. Both CPUs are synched & all LEDs are OK (all Solid Green) but we are not able to go online with the CPU.

Error 701-8004250A.jpg Logix5000 task monitor _SS01_01 (4).jpg Logix5000 task monitor _SS01_01 (5).jpg ControlNet_SS01_06 (1).jpg Rslinx.jpg
 
Yes I did from 3 other computers but the response is same.I also remove all HARMONY files, delete ETH driver. Restart PC & configure it again, But to no use.
 
receive data in DCS

What DCS ? Does it connect via ControlNet, Ethernet, or Modbus ?

The 100% CPU usage on the ControlNet module is almost certainly the heart of the problem. Figure out what's slamming the ControlNet and you may be able to free up enough resources to get online via the ControlNet network and bridge modules.
 

Similar Topics

Helloooooo. Help meee I have an Ethernet network ip. In the network is a 1969-L32E controller, within the architecture of the controller are two...
Replies
0
Views
1,903
Hi everyone, i have a Siemens S7-300 Cpu 314C-2 DP with several cards of i/o and servos my laptop has TIA version 16 and 17 loaded and...
Replies
3
Views
23
Hi guys, Im trying to set the real time clock in my Mitsubishi FX1N, but it shows this error ES: 01800001 I have good communication with...
Replies
3
Views
142
Hi, I am facing an error inside Omron Network Configurator. I have 2 PLC communicate each other using ethernet cable, send signal using Network...
Replies
2
Views
102
hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
Replies
2
Views
107
Back
Top Bottom