HMI delta and VFD LS control

wadi2000

Member
Join Date
Feb 2016
Location
earth
Posts
10
Hello

I have delta HMI and i want to control VFD LS SV-iG5A , i want to use MODBUS and control the inverter directlly from HMI. I did the control with DELTA inverter and every thing was ok
. But i wanted to do that with LS inverter but some problems , i dont know why there is no control.
All procedures i did with to communicate with LS from HMI delta as bellow :

At HMI editor

from Communication Setting

COM2 ----> Link2 -----> Controller (Delta Controller RTU)

and made buttons for stop and forwordrun and reverserun and numeric input

and at VFD i changed some parameters
drv =3
Frq=7
I59=0
I61=3
I65=1

i did all and communication was ok and no problem, but the problem when i want to put frequency input it not be acceptable and gives me default value 5057 and when i press foreword or reverse inverter can not take any response but there is no any error in HMI
If anyone made control with HMI and LS inverter type tell me how he did.
 

Similar Topics

Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
22
Hi, We have a customer that has an old DOP-A80THTD1 that is needed to be upgraded Can we upload from these units? Is there a special...
Replies
0
Views
94
Hello, I know little English, I want to use 4 plc cqm1 as slave (modbus), and hmi delta as master. Unfortunately, I cannot establish rs485...
Replies
3
Views
582
I'm trying to establish communication between an HMI DELTA (DOP-B07E515) and a PLC IDEC (FC6A-D16R1CEE) via the RS-232C/485 module (FC6A-SIF-52)...
Replies
2
Views
564
Hello, I'm facing a problem in communication between my delta TP70P-32TP1R HMI and DVP20EX2 PLC. I tried multiple ways in order to set the...
Replies
2
Views
1,326
Back
Top Bottom