I am stumped on this one and looking for some help.
I am working on a Modicon 984 processor. I recently added an 875-111 differential analog input card. The card is monitoring 2 chlorine and pH meters and 2 turbity meters. I am scaling the raw data in the SCADA software(Wonderware). The output for the turbity is perfect. I've tested the channels with a 4-20mA generator and the scaling is bang on. I've added these exact pH and chlorine meters to a separate 984 PLC without issue. Here is the problem:
When I connect the pH/Chlorine meter to the PLC the reading on the SCADA screen and the LCD on the unit do not jive. When I put a meter in series with the meter and the PLC, the 4-20mA signal and the SCADA screen perfectly jive. However, when I disconnect meter from the PLC and connected a 4-20mA reader to the wire leads of the meter by itself the 4-20mA signal is different (larger) and corresponds to the LCD display on the unit itself. Example: The unit has a 4-20mA test current function. When I put it to each of the settings with just the reader attached I get a perfect signal (19.97mA when on 20mA). However, when I wire it back up to the PLC with a meter in series there appears to be a distortion/or loss (16.85mA when on 20mA). It does not appear to be linear.
Also, note that the register in the PLC (0-4095) jives with what is being see with the meter (hence the scaling working). The meters have be calibrated and no offsets appear to be programmed.
Any help or suggestions would be greatly appreciated.
Tim
I am working on a Modicon 984 processor. I recently added an 875-111 differential analog input card. The card is monitoring 2 chlorine and pH meters and 2 turbity meters. I am scaling the raw data in the SCADA software(Wonderware). The output for the turbity is perfect. I've tested the channels with a 4-20mA generator and the scaling is bang on. I've added these exact pH and chlorine meters to a separate 984 PLC without issue. Here is the problem:
When I connect the pH/Chlorine meter to the PLC the reading on the SCADA screen and the LCD on the unit do not jive. When I put a meter in series with the meter and the PLC, the 4-20mA signal and the SCADA screen perfectly jive. However, when I disconnect meter from the PLC and connected a 4-20mA reader to the wire leads of the meter by itself the 4-20mA signal is different (larger) and corresponds to the LCD display on the unit itself. Example: The unit has a 4-20mA test current function. When I put it to each of the settings with just the reader attached I get a perfect signal (19.97mA when on 20mA). However, when I wire it back up to the PLC with a meter in series there appears to be a distortion/or loss (16.85mA when on 20mA). It does not appear to be linear.
Also, note that the register in the PLC (0-4095) jives with what is being see with the meter (hence the scaling working). The meters have be calibrated and no offsets appear to be programmed.
Any help or suggestions would be greatly appreciated.
Tim