Micrologix 1400 to PVC600 Communication by RS485 port problem

nilesh_1106

Member
Join Date
Dec 2011
Location
pune
Posts
34
Hi..

I am using Micrologix 1400 PLC & C600 HMI. I want to do the communication between them by DH-485 via RS485 port.( As distance between them is 40 meters apart )
I already set the Channel 0 of micrologix 1400 to DH-485 and also I have 1763-nc01 cable. but I don't know about c600 RS485-port connection & setting for the same.
So kindly help me out for this problem..
 
Part 1 - MicroLogix 1400>DH-485>PanelView Component C600

nilesh_1106 said:
...I already set the Channel 0 of micrologix 1400 to DH-485 and also I have 1763-nc01 cable. but I don't know about c600 RS485-port connection...

Hi,

You are using a 1763-NC01, so you are connecting to channel 0 on the ML1400, which is an isolated port. If you are only connecting the PV-C600 to this isolated port, then you can connect your cable point-to-point between the PV-C600's non-isolated RS-485 port and the isolated RS-485 port on the ML1400, via the 1763-NC01.

The recommended cable for this connection is Belden 3106A or #9842 or equivalent.

The RS-485 port on the PV-C600 has a built in 121Ω terminating resistor between the R and R- terminals.

The link between the TERM and A terminals on the 1763-NC01 terminates the built in 120Ω resistor for the MicroLogix end.

I've pulled the attached diagram together to try and clear up the wiring for you...

ML1400_DH-485_PVC600.jpg
 
Part 2 - MicroLogix 1400>DH-485>PanelView Component C600

nilesh_1106 said:
...& setting for the same...

If you have Connected Components Workbench software (CCW) installed, open PVc DesignStation to create an application for the PV-C600. Configure the communications settings, PLC tags, display screens, etc. for the terminal in PanelView Explorer, which is the design editor within PVc DesignStation.

See the attached screenshots of the driver configuration, and tag setup screens in PanelView Explorer.

G.

CCW_PVC600_DH-485.jpg CCW_PVC600_TAGS.jpg
 

Similar Topics

I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
62
Hi, I am working with a Micrologix 1400 model 1766-L32BXB. With no input wires connected to the “in12” thru “in19”, I am getting 24 volts while...
Replies
4
Views
219
Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
Replies
4
Views
285
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
Replies
8
Views
605
I'm not super familiar with the Micrologix line of processors, but I am pretty familiar with RSLogix 500. I'm trying to simply copy a string to...
Replies
4
Views
297
Back
Top Bottom