Micrologix 1400 Modbus RTU RS485

Raul_Robins

Member
Join Date
Sep 2013
Location
mexico
Posts
3
Hi everyone,

Im new using modbus and i have some toubles im trying to communicate a micrologix 1400 and a device Satec pm130 via modbus and using the 1763-NC01 cable but it doesn´t works. Can anybody help me Please.
the satec terminals only have rs485+ , rs485- and Shield.
and de 1763-NC01 Term, A, B, Com, Shld, cgnd.


Thanks

20150102_225116912_iOS.jpg 20150102_225125204_iOS.jpg
 

Attachments

  • Rail_Welding_Machine.zip
    27.7 KB · Views: 49
I’m pretty sure A and B are the ones used when the port is configured for RS485. Keep in mind that you need to configure the channel 0 port to be RS485 (it defaults to RS232). You may also need to swap A and B around.
 
As Firejo said...

See picture. Set channel 0's "Protocol Control" to "No Handshaking (485 network)

configurecontrolline.PNG
 
Hi Mickey ,
I Set channel 0's "Protocol Control" to "No Handshaking (485 network) as you say and works!!! thanks I will continue testing and told them the results.

Thanks a Lot!!
 

Similar Topics

I want to learn about modbus communication and I saw on another thread about inexpensive modbus relay units so I found it on Amazon along with a...
Replies
46
Views
7,187
I have a spare Micrologix 1400 Series B I bought used on Ebay awhile back. I had thought of it as a spare PLC for my train project but I screwed...
Replies
4
Views
1,235
Good Day! Would anyone be able to explain what is happening with the COP's and MOV's in this Modbus poll routine? If anything I am confused by...
Replies
6
Views
1,726
I been tasked with setting up communication between a heating cooling unit manufactured by Advantage Engineering and a Microloagix 1400 plc. The...
Replies
6
Views
2,495
Hi, I am trying to communicate between a MicroLogix 1400 and a Click PLC. There is a great video from AD that shows the simplicity of...
Replies
2
Views
1,759
Back
Top Bottom