I use the input card 1746 NI16I (class 3)with an SLC 504 on a 13 slot rack and run into this problem during the test:

All channels have the same configuration:
Input Type: 0-20mA
Filter frequency: 40Hz
Data format: 1746-NI4 Data Format
On each channel, I put a source of 0, 4mA, 12mA, 20mA and check the input values.
For all the channels, the result is correct (0, 3277, 9830, 16383)
But at the channel 11, I receive these values
(0, 4000,12000,20000)
Does this means the card is not good? Or may be some other configuration details are missed?

Please advice
Thank you very much
 