AB Micrologix 1400 to Schneider Magelis HMI

Marie1982

Member
Join Date
Feb 2007
Location
House
Posts
121
Hi,

We want to use a Micrologix 1400 with a Magelis over Ethernet. In the Magelis, we use AllenBradley Ethernet/IP for Micrologix. We can read ok but when we try to send values from the Magelis to the PLC, the PLC returns error code 1B.

Anyone has an idea?

We use built-in Ethernet ports on PLC and HMI.
 
Hi Marie1982,

I got your PM, but I'm very busy at the moment on a project trying to solve my own issues.

Off the top of my head -

In Vijeo Designer, what "Sharing" properties are set for the variables you are trying to write to in the PLC? They should be set Read/Write if you want to write to them?

Regards,
George
 