B&R 4PP045 Calibration needed.

Join Date
Oct 2015
Location
Amsterdam
Posts
9
Hey guys,

I have a annoying problem with our'e 4PP045...Power Panel of B&R.
The touch is shifted to the left side of the screen, so it needs to be recalibrated.

Could somebody tell me how to program a calibration button (or something)?
I have AS3.0.90.34, a complete project is also welcome ;)

Thanks in advance,
 
Well, the VisAPI library can trigger calibration from the program or you can add a button to the HMI and set the action to Calibration. Couldn't be easier really.

We typically set a spare input to trigger a calibration since having a button buried in the HMI is not very useful if the calibration is so off you can't press it.
 
Oke thanks for the info,

I started searching in the help file of AS (which is pretty good) and find the button you talked about.

However is it possible to implement this button (spare input) in an already existing program without having a source code?

Greetings,
 

Similar Topics

Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
84
Hello, I have a problem calibrating siwarex ms with siwatool ms Whatever I have tried, I have communication error and numerous retries to...
Replies
0
Views
74
Hi everyone, i hope you are doing well i am using fbs 2lc module , i have calibrated the weight by calibrated weight but my value is not...
Replies
0
Views
85
5069 IF8 with a 4-20ma 0-100psi, sealed fixed, no calibration, transducer attached. IF8 is scaled 4ma= 0 psi, 20ma=100psi. If over time the...
Replies
12
Views
2,601
I am in need of a calibrator to provide a variable 0-5 vdc output? any suggestions? Thanks
Replies
5
Views
1,647
Back
Top Bottom