we are converting PLC-5 controls with control logix system.
The idea is to replace only PLC 5 processor and retain all existing PLC I/Os. Most of the PLC I/Os are available in Remote Chassis and are connected using conventional 1771-ASB Remote I/O Adapter. Under conversion program we will connect all existing Remote I/O chassis using 1756-RIO adapter, with new Control Logix processor. So far we could not understand how PLC Discrete I/O's can be accessed in Control Logix program?

PLS Help !!!!!!.
Thanks.
 
hi technut

Its quite easy, open RSlogix 5000 and build your IO configuration. Apart from your processor you have to add a 1756-DHRIO module. With this module you add your 1771-ASB adapter, select this and then add a generic IO module. You have to select your addressing type in the properties of 1771-ASB.

You can add generic modules to this adapter and then create tags to access the inputs and outputs...

Hope this is of some help...
 

Similar Topics

Hi Siemens guys! I am experiencing SF fault on our S7-300 (6ES7 315-2AH14-0AB0) CPU from time to time. I've checked the diagnostic buffer and...
Replies
13
Views
162
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
Replies
2
Views
80
I have to provide remote access and control to a touch screen. I was thinking about using Weintek and the Weincloud. Does anyone know if this is...
Replies
11
Views
594
Greetings, I am working on a project and I would like to scale %AI to -10.0 to 10.0 VDC. The module Input data is stored as a 16 bit Integer and...
Replies
4
Views
66
Hi all Trying to remotely connect to a TIA Portal PLC. I can ping it without a problem but can't get my software to connect. I've opened port...
Replies
8
Views
324
Back
Top Bottom