-Channel 0 as the modbus master port
-8 slaves (Yaskawa VFD's) on a RS-485 multi-drop network
-I can talk to the slaves (Yaskawa VFD's) through MD Bus by acting as the master ( modbus testing software ) so I know the network is good and the converter.
-The 2 wire RS-485 wires go into a RS-485 to RS-232 converter then into the PLC (CH 0).
-I have the master message instruction set on a 5 second timer and have the instruction set properly with the correct slave address, and modbus holding registers
-I have changed the CH 0 comm config (ie. No handshaking, rs 485, etc)
-The message instruction comes with an error "message time out" and no values show up in the registers I assigned in the message instruction?
What am I missing?