To start I have read two days worth of past messages, but I haven't found quite the right answer yet, hopefully someone can help me. The project i'm working on is I have a slc 5/04 on a dh+ network with two other plc 5/20 processors, but I have installed new panelviews (c-more) from automation direct. The new panelviews are ethernet, so what I have done (because I have to keep the dh+ network) is build a dedicated ethernet network by using a switch to put the four panelviews on, connected to a net-eni card to feed the information into the slc 5/04. I have one panelview talking directly to the net-eni ip address and the other panelviews talking the the main panelview. It works great with only 3 panelviews on then when I put the 4th on because the net-eni is a serial cable to the slc 5/04 it has to be bogging the comm rate down to where the inputs take forever to acuate or not at all. So now I have installed a partial contrologix rack with a dh+ card and a ethernet card because I read you can brige with this setup. How do I create the path to get the information into the slc, I was told to use the (msg) instruction but, or in the rslogix5000 software do I have to create some kind of link between the two cards and If I do that how do I give the slc an IP address to send the informatio to? Any advice would be greatly appreciated.