Hello,
I'm running my Plc in PLC Simulator (Unity Pro XL).
Intouch sees the connected links but the tags are not matching
(+1 on InTouch)..
example :
Intouch : %MW1950 Equals %MW1950 on the PLC datas.
I've been told it has something to do with the NodType.
It was set to Modbus by default, since most of our other plcs on the network are configured that way. This one PLC is Tsx premium..
Is there a way to adjust the starting address, either on Unity or SMC perhaps?
Thank you for your hindsights!