Differential Pressure (DP) for level has been used for probably 80 years now. It is a mature liquid level measurement technology.
A dual port DP transmitter is used in 99.9% of applications because the DP transmitter read fractions of an inch of water column DP at static pressures of 2000 psig. The high side port connects at the bottom, the low side port at the top of the vessel, and a tube/pipe is run from the vapor space above the liquid level down to the transmitter to the low side port to measure the working/static pressure.
Access ports can be pipe taps but a tank designed for a lower mounted DP transmitter will probably have a 3" flange at the bottom. The typical sensing diaphragm on a flange mount is a 2" diameter diaphragm (the wider the diameter, the more sensitive the pressure measurement).
Some limitations are
- level below the bottom tap can not be sensed, only liquid head above the bottom tap creates a readable pressure.
- head pressure is directly proportional to the density (Specific Gravity) of the medium. If the medium density changes, the change in density is a proportional error: 4.5% change in density is a 4.5% error in level.
- subtracting 2 gauge pressure measurements typically does not provide sufficient resolution. Rosemount has a set of two 'matched' gauge pressure transmitters that communicate between each other, one of them subtracting the low side from the high side to produce a level output. Technology is maybe 12 years old now.
- Temperature limitations on the diaphragm fill fluids (behind the diaphragm), specifically at vacuum pressure in the vapor space (spelled out in mfg specs)
- condensation in the tube/pipe running from the top side down to the transmitter located at the bottom can build-up and cause an offset error.
- liquid movement from an agitator or in/out flow can exert a force on the sensing diaphragm that is not hydrostatic head, an error in a level measurement.
Is there an access port at the bottom from which the pressure can be tapped? What's the working/static pressure in the vessel? Is the medium friendly (non-corrosive) to stainless steel? How hot/cold is the process?