wildswing
Hey fellas,
I'm looking for ideas. I've been asked to look into creating a system that will measure the length of panels cut by our flying cut saws. I'm most likely on a tight budget (no I don't know how much yet).
Here's some details...
- continuous MDF press followed by flying cut saws. Panels accelerate away after cut. Panles to be measured immedaitely after being cut as they pull a gap.
- panel lengths vary from 16' to 24'.
- panel speed where we intend to measure: The leading edge can vary anywhere from 20 fpm to 120 fpm (press speed) while the trailing edge (after cut) will accelerate to approx 220 fpm.
- accuracy of +/- 1/8" would be lots.
- overall process is controlled by an AB PLC5/40. Processor rack is 200' away in mcc room. There is RIO near where measurement will be done.
- We tried this with a SLC, a HSC module, an encoder mounted to a homemade wheel and a laser as an edge trigger. It worked pretty well, but (according to the guys who where working the project) it takes too long for the HSC module to report the mumber so we couldn't get an accurate length.
- I need to get the measured length to the PLC5 somehow
Ideas I'm tossing around:
- Low end CLX, HSC, encoder, DC input trigger, DHRIO (like the SLC setup but with CLX hardware this time) Overkill?
- 1771-VHSC in an old 1771 rack (but it's update rate is 100 ms, that's slower that the slc HSC we tried)
- what about Compact, Flex or MicroLogix? I have no experience with these? Can they talk RIO? How about serial to the PLC5 CH0?
- are there any solutions "in a box" out there?
Any ideas you fellas can toss into the ring would be very much appreciated. Thanks.