Hi all,

To begin, I'm using a stand-alone (not on any kind of network) PowerFlex 40-P , a Panel Mount LCD HIM (Allen Bradley Cat. No.: 22 - HIM - CS2 Series C) and an external Control Station which has start/stop momentary Push-Buttons (each with a Normally Closed and Normally Open Contact) and a 10kΩ potentiometer for speed reference. I don't have access to a PF drive or I'd go ahead and try it out for myself.

My main question: If I'm using the 3-Wire SRC wiring scheme (in reference to my start/stop control, pictured below), and I wire my momentary stop to be normally closed, will this quick "LOW" pulse to the stop input (Terminal 01) tell the PF40P to stop the motor or would the stop button be required to be maintained in the off/disconnected position? The "Input/Output" section, in the picture, mentions that you can use a momentary N.O. start push-button, but doesn't really specify if the stop can be momentary or if it has to be maintained.

If the stop push-button must be maintained, is there a way to program one of the Digital inputs so that I could wire my momentary stop PB to one of those and configure the drive to stop each time it receives a HIGH signal from it?



Thanks in advance!

-Jeff

PowerFlex40P.png
 
In this setup, the Stop would be momentary. There is an internal seal-in circuit around the Start input to make this a true 3-wire control circuit, so that if there is a power failure, the Start button would need to be pressed again.
 

Similar Topics

Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400 Messaging but don't see the N...
Replies
4
Views
221
I'm in the process of replacing an existing powerflex 40p. The old one died with no software backup but we did have a printout of the parameters...
Replies
3
Views
1,201
How can I find the IP of a used Powerflex 40p? I have used them in the past I have a hand held programmer for the 22 Comm E that I used before...
Replies
4
Views
1,752
Is there a way in rsnetworx or connected components to compare 2 powerflex parameter sets? TIA P.S this is also my first post here so hello...
Replies
5
Views
2,176
I have P036 configured as 2 wire SRC Control with an exteranl supply. I choose the direction with a 3 point rotary switch. The problem is when it...
Replies
1
Views
1,150
Back
Top Bottom