Powerflex 527 CiP drive and Safety Signature

I swapped out a PF 527 drive that has been giving me occasional faults.
I replaced with a new 527, assigned its IP and gateway and cycled power.

When it powered up I could go online with controller via Studio5000 but had an I/O fault (blinking green light) and lost communication to all the drives. They all had the little yellow exclamation mark next to them.

I recall that this has something to do with the safety signature not being assigned to the new drive.

Problem is I can't connect to any module in order to change it.

Anyone care to shed some light on the procedure of how to reset this mod fault?

I ended up just putting the bad drive back in until I figure this out.

Thanks
  Reply With Quote
Old June 23rd, 2022, 12:55 PM   #2
DarrylR
Member
United States

DarrylR is offline
 
Join Date: Nov 2019
Location: illinois
Posts: 52
Search 520-UM002C-EN-E for the PF-527 manual. Chapter 3 should have all the info you need. Could be a power structure mismatch, or need to set compatible module for electronic keying.
  Reply With Quote
Old June 23rd, 2022, 01:26 PM   #3
PiperJohn
Member
United States

PiperJohn is offline
 
Join Date: Mar 2022
Location: Michigan
Posts: 46
Thanks I'll take a look.
It's a 5380 safety controller so I thought it was it wasn't seeing the safety signature in the new drive.
  Reply With Quote
Old June 25th, 2022, 08:50 AM   #4
PiperJohn
Member
United States

PiperJohn is offline
 
Join Date: Mar 2022
Location: Michigan
Posts: 46
To answer my own question;
Yes, I/O fault was caused by Safety network number.

Right click drive replaced to open module, click box with dots (...) under general tab, then click set. Yes, to accept. Then cycle power to the drive.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Safety FLT S03 Powerflex 527 helphelphelp LIVE PLC Questions And Answers 2 August 21st, 2021 11:45 AM
Powerflex 525s, Safety Circuits and monitoring testsubject LIVE PLC Questions And Answers 18 February 4th, 2021 10:43 AM
PowerFlex 525 and Safe Torque-Off Circuits Cydog LIVE PLC Questions And Answers 17 November 21st, 2018 10:14 AM
Trying to understand safety PLC's (specifically Siemens) Jieve LIVE PLC Questions And Answers 3 June 24th, 2014 09:27 AM
PowerFlex 70 Safety Circuit aiki202 LIVE PLC Questions And Answers 8 December 7th, 2010 09:13 AM


All times are GMT -4. The time now is 10:08 AM.


.