Safety relay - diffrence between power on and emergency stop

Hi,

We have a machine that we wan't to restart after power on if the emergency stop is OK. But if the emergency stop is tripped with the button we wan't it to be resetted with the E-STOP. Is this something what i achievable? We don't have personal on site so after power failure we wan't it to restart.

/Tim
  Reply With Quote
Old June 23rd, 2022, 05:31 AM   #2
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 4,025
It depends on the Relay, most have an input for a reset button, it will depend but if this is linked out it turns it into auto reset, some have another input again linked to auto reset, I suggest you download the manual for the unit & it should show the auto reset.
Here is one for a Pilz unit.
Note: Auto restart can be dangerous, even if no personnel are in the location there are certain measures that need to be taken for example a sign stating machinery will start automatically, also other precautions in the event of a fault.
Attached Images
File Type: png Pilz type.png (37.2 KB, 136 views)
  Reply With Quote
Old June 23rd, 2022, 05:34 AM   #3
rQx
Lifetime Supporting Member
Sweden

rQx is offline
 
Join Date: Oct 2010
Location: Trelleborg
Posts: 965
Quote:
Originally Posted by parky View Post
It depends on the Relay, most have an input for a reset button, it will depend but if this is linked out it turns it into auto reset, some have another input again linked to auto reset, I suggest you download the manual for the unit & it should show the auto reset.
Here is one for a Pilz unit.
Note: Auto restart can be dangerous, even if no personnel are in the location there are certain measures that need to be taken for example a sign stating machinery will start automatically, also other precautions in the event of a fault.
I know there is auto restart function, but I wan't "both".
Manual restart when emergency stop is pushed
Auto reset if power is applied (and no emergency stop pushed)
  Reply With Quote
Old June 23rd, 2022, 05:38 AM   #4
TurpoUrpo
Lifetime Supporting Member
Finland

TurpoUrpo is offline
 
Join Date: May 2008
Location: Switzerland
Posts: 1,552
First, why?

Think about scenario - someone presses e-stop, resets the e-stop button (not the relay) and someone powers off the system and the powers on.

Do you want it to automatically reset the safety on that situation?

Second, are you sure that is even allowed. What I remember working with safety it has always been - power on, check everything is clear and safe - reset safety and just then power on the machine.
  Reply With Quote
Old June 23rd, 2022, 05:41 AM   #5
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 4,025
The only thing I can suggest is you put in a N/C contact in series with the auto reset but it has to be a mechanical latched e-stop, so only when it is released it will start. or use a separate e-stop relay & safety relay slave one off the other.
Not ideal but will work, seen this on batching vessels, the e-stop circuit is separate from a lid safety relay although in this case the e-stop stops everything but the lid safety only disables the agitator.
  Reply With Quote
Old June 23rd, 2022, 05:48 AM   #6
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 4,025
Doh, so simple use a lock off e-stop button so if pressed then it requires an operator to reset it, simple.
  Reply With Quote
Old June 23rd, 2022, 05:50 AM   #7
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,720
Not commenting on the 'should you' bit, the 'can you' bit can be done with an on-pulse timer. It closes for a short time at power up, you parallel the 'normally open' contact with the reset button. Though it depends on what checking the Emergency Stop relay does at power up.
__________________
Knowledge is power, share the knowledge.
  Reply With Quote
Old June 23rd, 2022, 09:09 AM   #8
janner_10
Lifetime Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 1,269
Not much info to go on.

I doubt you can achieve this programmatically with a basic safety relay as it would look for an edge transition, but you certainly can with a safety PLC.

If it's just for short term power outages then I would just use a UPS for anything of any length of time I would probably use a Auto / Manual restart key switch for when the site is unmanned and manned.

Risk assessments and visible signage are going to be a must, along with training around auto restart.

For example, not much wrong with auto restarting a remote pumping station or HVAC, but you wouldn't make that argument with a mechanical press for instance.
  Reply With Quote
Old June 23rd, 2022, 10:57 AM   #9
ValeoBill
Member
Canada

ValeoBill is offline
 
Join Date: Aug 2019
Location: Wasaga Beach, Ontario
Posts: 78
If you want the manual control to bypass the safety circuit, what's the point of having it? As others have noted, an autoreset can be done with most safety relays. Not sure where you're from but making such changes here would require risk assessment and engineering approval. Be careful...
  Reply With Quote
Old June 23rd, 2022, 12:41 PM   #10
Rson
Member
United States

Rson is offline
 
Join Date: Jun 2017
Location: Michigan
Posts: 493
Do you have relays only in this panel or are you using a PLC?

If you are using a PLC, just wire a control power reset relay into the safety circuit. Read the E-stop as an input, control power as an input, the safety reset pusbutton (if applicable) as an input, and write your logic for your conditions.

The above is not using the PLC as a safety relay - it is only using it as a means of resetting the safety relay.
  Reply With Quote
Old June 23rd, 2022, 01:21 PM   #11
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 4,025
I think the OP means that on a power loss, the safety relay should automatically reset as this is an un-manned station.
There is only a need to use a e-stop with latching (preferably key release) and make the circuit auto reset, if the e-stop is pressed, then it latches in and cannot reset until the e-stop is released, in the event of a power down the relay will auto reset. perhaps the OP could clarify this.
  Reply With Quote
Old June 23rd, 2022, 01:27 PM   #12
janner_10
Lifetime Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 1,269
Didn't think of that. I guess a bit more robust than a key on the front of the panel.

(Until it's in someone's pocket and they are in the pub!)
  Reply With Quote
Old June 23rd, 2022, 05:47 PM   #13
QvixoteRoux
Member
Mexico

QvixoteRoux is offline
 
Join Date: Jun 2014
Location: Reynosa
Posts: 87
By safety standars any machine at power ON must have all safety devices manually reset (when they are configured for manual reset)


If this is not going to be considered, make it with the PLC logic, at first scan check if the E-stop(s) are correct then start the machine, if not wait until reset


I should have not said that last part since I once had a valid CSME (valid 2016-2020)
__________________
Mexican, need to practice engrish, please cooperate

Industrial Engineer working as PLC programmer.
---
"Everybody believes what is easier for them to believe"
  Reply With Quote
Old June 23rd, 2022, 06:48 PM   #14
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 3,559
I had to implement this once. We had a process where the consequences of not automatically restarting after a power failure were significantly more severe than the automatic restart. There were zero exposed moving parts, and significant chemical hazards involved if the fans weren't running.

What we did was to leave the safety relay in monitored manual reset, but to wire an output relay from the PLC to permit the PLC to reset the safety circuit, in parallel with the physical reset pushbutton.

Inside the PLC logic, we had a latched bit which monitored the state of the safety relay. At power up, we checked the bit and the logic essentially said "if, and only if, the safety relay was healthy when the PLC went down, try exactly once to reset it 5 seconds after power on".

This means that if the safeties were tripped when the power went off, the safeties stayed tripped when it came back on. If someone presses an e/stop while the power is off, safeties remain tripped when the power comes back on*. But if the safeties were healthy when the power went out, and no e/stop was pressed when the power came back on, the safety circuit would get reset and the system would auto restart.

(*provided the e/stop wasn't both pressed and reset again while the power remained off).


Of course, you absolutely must do an extensive risk assessment and document, document, document. If you had any guarded areas, I personally would never sign off on this. If you had any exposed moving parts, same deal, even if they were protected by light curtains. My application was closer to a laboratory environment than an industrial environment, so the level of physical/mechanical hazards present permitted the idea to be entertained.
  Reply With Quote
Old June 23rd, 2022, 07:24 PM   #15
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Nashville, Tennessee area
Posts: 3,339
a risk assessment must be done and approved before trying to do this.

i have reread your post and the risk assessment still needs to be done.
i think some sort of warning buzzer needs to be in place to alert someone that the machine is going to start.
james
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -4. The time now is 09:33 AM.


.