Factory Talk View is Slow

Monroe1982

Member
Join Date
Feb 2016
Location
Texas
Posts
3
I have a network distributed application running on a windows 2008 server 64 bit with 12 gb ram. 3 Clients are on mini HP windows 7 64 bit with 8 gb ram. I migrated the project in from rsview. The response time is very slow. I can click a button that toggles a bit in plc 5 and it takes close to 2 seconds to set the bit then another 2 seconds to update the graphics display. I have the page update rates at .05 and have tried several different speeds to see if it helps any with no luck. Even direct addressing is too slow. I have one simple page running in the back ground with a simple single line of vba to handle the internal annunciation for alarms. Has anyone found a solution for this problem yet? I have read through all the post I can find with no luck. The licensing that was purchased for this is outrageous so I need to figure out a way to make it work. Help please!
 
FIx

For whatever it is worth we finally found somewhat of a solution. Rslinx enterprise does not do well with plc5. Switch to rslinx classic OPC servers.
 
If all your screens and devices are set to a refresh rate of .05, wouldn't it bog the system down with all that traffic?

I had 3 pv+ terminals running to a slc 5/05 with a screen refresh rate of .25 with no issues. each had about 50 screens and over 150 pb's / switches

james
 
Is the system live? If yes, can you stop it to run tests?

I would create a test project (1 screen, 1 push button and 1 numeric input). See what kind of response times you can get with that.
ex. using RSLinx Enterprise vs. Classic
ex. different update rates for the display


What version of FTView?
 
BTW, direct reference tags will always give you a better response time versus HMI tags.

HMI tags are 2x slower than direct reference tags (for read updates).
That's true for all update rates.
 

Similar Topics

Hi all, Attached below is an example of what is happening to our existing SCADA. It seems after patching some Rockwell Software that I thought...
Replies
9
Views
319
The client has an application that when communication between the PLC and the Factory Talk VIEW supervisory fails, the object in the supervisory...
Replies
5
Views
284
Hello all, I am looking for a way to have a user get logged out after an X amount of time because to default so that user privilages are no...
Replies
4
Views
586
Hello everybody. I was wondering if there is a way in FTVIEW Studio to close ) view after x min without interaction . My issue is the following...
Replies
2
Views
363
Is there a way to choose the base font in ME. Text in the Arial Unicode MS which is the default font on my FTVS doesnt show up properly on a...
Replies
1
Views
674
Back
Top Bottom