Hi all!

I got a newby question for you: I need to time multiple events individually in Siemens S5-95U. To do that, a timer generates a pulse every second. That timer is placed in a function block called by OB 1. Is this good practice? Should I use multiple timers for each event?

Thanks in advance,
Arthur

Post Scriptum: Timing doesn't need to be very precise, the maximum time count is around 10 hours.
 
After experimenting, the conclusion is: using a single timer to generate a pulse train and using this pulse train to time events isn't very accurate. If you don't need very high resolution and is willing to have 10s/min error, it's a solution that saves timers.
Another solution I tried was using OB13(periodic call) to generate those pulses. Again, there was error, but this time much smaller (0.00833s/min).
Undoubtedly, using an individual timer for each event is the more precise solution.
 
I am not familiar with S5. They are very old.
Many older types have issues with the restart of the program cycle.
Normally use a pulsed time signal. Then an add block
Add one to a register every second. Then compare that number.
Shouldn’t have errors then
 
There is a built in word with bits that flip every 10s 1s 0.1s etc that you can use for that purpose. It should be extremely accurate.

I don't think S5s have that clock byte like S7s do...
Well, I know S5-95U doesn't!
Even so, I used this approach in a S7-300 and got great results!
 
If you get desperate you can accumulate the scan times until you add up to your preset then start accumulating with the remainder after subtracting your interval. There will be some jitter but the average interval should not drift.
 
If you wanted something more accurate then you could connect a more precise time signal to an interrupt enabled digital input and count those pulses.

Nick
 
I hope you have spare parts for this old S5 system. I have a couple of cpu' s and many input and output cards and software. I am replacing these systems as there old and obsolete. But there very reliable and they are still in use around the world.
 

Similar Topics

Hello, I am struggling to figure out some logic. I have an analog pressure sensor coming into the PLC and would like to have multiple timing...
Replies
4
Views
129
the plant I am supporting uses a siemens graph function to do some of the step procedures. in several steps it waits for the step to execute for...
Replies
1
Views
755
All Using a MicroLogix 1400. Not a huge program doing an auto stop function based on a calculated roll diameter Using encoder feedback for...
Replies
12
Views
3,191
Hi all, I'm trying to fully understand the different effects of the Loop Update Time parameter within the Logix PID instruction. I was always...
Replies
18
Views
4,548
Logix 1756-L82E processor. I am using the .ST bit to time how long a MSG takes to complete. This works fine except for every 10th MSG cycle takes...
Replies
5
Views
1,611
Back
Top Bottom