3P + N + E with E and N the same

Hi, I'm at commissioning where not everything was discussed prior to my arrival. My unit has a 3P + N + Earth connector but at site they have 3P + Earth but they say the neutral and the earth are the same.

So can we then in the connecting cable to our unit simply bridge the earth and neutral core in the female contact at our end of the cable? My cabinet will then have its original connector w 5 terminals and the site will have the existing with 4 terminals.

Thanks in advance
__________________
Jon Bolmstedt, Inspired Automatician.
  Reply With Quote
Old April 19th, 2018, 10:59 AM   #2
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 557
I wouldn't do that personally, although they will be connected together on the authoritys' side somewhere.

If you don't need the N just swap your connector over, if you do, then someone will have to supply one!

You're not the first and certainly wont be the last!
  Reply With Quote
Old April 19th, 2018, 11:47 AM   #3
spaderkung
Member
Sweden

spaderkung is offline
 
Join Date: Aug 2007
Location: A flat type "4"
Posts: 319
Thanks. We need the N because we run several internal devices on one phase each.

What are the the risks that you see?
__________________
Jon Bolmstedt, Inspired Automatician.
  Reply With Quote
Old April 19th, 2018, 11:57 AM   #4
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,675
Quote:
Originally Posted by spaderkung View Post
Thanks. We need the N because we run several internal devices on one phase each.

What are the the risks that you see?
The ground conductor between the service and your equipment will be carrying current. This is a no-no.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old April 19th, 2018, 12:05 PM   #5
Dirt
Member
Sweden

Dirt is offline
 
Join Date: Apr 2008
Location: Stockholm
Posts: 153
As said above; No current through PE on purpose..

(Unless you're a Grid Operator using a PEN-system, which you're not)

Risks?
3W + PE cables are not designed to carry max current continuously through PE. And it's simply not allowed either.

Isn't there going to be a third party electrical inspector there after installation of new equipment? Pretty standard in the power and process industries in Sweden at least.

Last edited by Dirt; April 19th, 2018 at 12:19 PM.
  Reply With Quote
Old April 19th, 2018, 12:11 PM   #6
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,198
It is more of an installation type question rather than PLC, an installations forum may give you better answers.

The system you describe is a recognised and valid system called TN-C, and as OkiePC says the combined Neutral/Earth can carry current. I don't know enough to say if it is good or bad, but it does exist and it is valid.

https://en.wikipedia.org/wiki/Earthing_system
  Reply With Quote
Old April 19th, 2018, 12:23 PM   #7
LadderLogic
Member
United States

LadderLogic is offline
 
LadderLogic's Avatar
 
Join Date: Jun 2003
Location: Chicagolandia
Posts: 1,256
I'd feel safer adding a transformer (380 to 220 as I assume this is in Europe?) for single-phase devices.
__________________
Don't trust, don't fear, don't beg...
  Reply With Quote
Old April 19th, 2018, 04:58 PM   #8
AustralIan
Member
United Kingdom

AustralIan is offline
 
Join Date: Jan 2013
Location: UK
Posts: 689
+1 transformer, or replace components with 400V 1 phase versions.
  Reply With Quote
Old April 19th, 2018, 05:05 PM   #9
Maxkling
Member
United States

Maxkling is offline
 
Join Date: Mar 2011
Location: Atlanta
Posts: 143
Quote:
Originally Posted by OkiePC View Post
The ground conductor between the service and your equipment will be carrying current. This is a no-no.
Exactly. If this conductor becomes broken or disconnected and your panel has no path then you have potentially energized every metal surface of the panel.

Also if the switchgear or PDP has ground fault monitoring then it will cause issues.
  Reply With Quote
Old April 20th, 2018, 03:38 AM   #10
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,191
Quote:
Originally Posted by spaderkung View Post
Thanks. We need the N because we run several internal devices on one phase each.
What are these devices ? How much power ?
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old April 20th, 2018, 03:50 AM   #11
ktmtragic
Member
Australia

ktmtragic is offline
 
Join Date: Jan 2013
Location: Sydney
Posts: 61
NO DON'T DO IT !!! Deadly !
  Reply With Quote
Old April 20th, 2018, 05:19 AM   #12
spaderkung
Member
Sweden

spaderkung is offline
 
Join Date: Aug 2007
Location: A flat type "4"
Posts: 319
Thanks. Will verify if it is a PEN and have a local electrician to come.
__________________
Jon Bolmstedt, Inspired Automatician.
  Reply With Quote
Old April 20th, 2018, 06:23 AM   #13
Dirt
Member
Sweden

Dirt is offline
 
Join Date: Apr 2008
Location: Stockholm
Posts: 153
Quote:
Originally Posted by spaderkung View Post
Thanks. Will verify if it is a PEN and have a local electrician to come.
If it's a real PEN (which it most probably isn't), you have to separate it to PE and N in your cabinet before using any of it for your consuming equipment and probably add a GFCI (JFB). Much like the same way you you would do in a service panel.

Typical in Sweden is that you get 3 phases + PEN from the grid then at first service panel PEN is separated into PE and N. PE can NEVER EVER be used again as PEN. That's why it's very very unlikely you have a PEN supplied for your equipment.

Last edited by Dirt; April 20th, 2018 at 06:41 AM.
  Reply With Quote
Old April 20th, 2018, 04:46 PM   #14
ktmtragic
Member
Australia

ktmtragic is offline
 
Join Date: Jan 2013
Location: Sydney
Posts: 61
The Neutral needs to come from the supply. The customer can pull a single core cable in for that. The neutral connection originates at the customer main and unless it is a separate installation it may not originate from anywhere else
  Reply With Quote
Old April 20th, 2018, 05:50 PM   #15
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 823
I'd personally pull a new 5 core cable. Less confusion.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 09:40 AM.


.