I have / had a a PLC controlling a Yasakawa 1000 VF down to 16 hz .
The VFD continues to give me a OV fault (over Voltage)
The load is CONSTANT. The fault is intermittent. You can see up to 15 hours of run time before the fault occurs. (we are not ramping up and down and it's not on startup or shut down.
I removed the PLC and am now running it as a stand alone drive at a static speed and the problem persist.
Yaskawa tech support says it's "motor issue, wiring or frequency within the building"
The equipment manufacturer assure me the motor is not limited by the low speed. and the motor has a Inverter Duty rate of 10-90 HZ So I eliminated that.
I have temp wired directly between the output of the drive to the motor to eliminate any wiring issues.
The motor is a Bodine Motor "pacesetter" Inverter duty motor wired for 460.
And at 16 HZ you are getting 460 in and 120-130 ish volts out, which matches my math as appropriate (460/60 = 7.60) ------ 16 hz X 7.6=121.6 volts
Any ideas?
The VFD continues to give me a OV fault (over Voltage)
The load is CONSTANT. The fault is intermittent. You can see up to 15 hours of run time before the fault occurs. (we are not ramping up and down and it's not on startup or shut down.
I removed the PLC and am now running it as a stand alone drive at a static speed and the problem persist.
Yaskawa tech support says it's "motor issue, wiring or frequency within the building"
The equipment manufacturer assure me the motor is not limited by the low speed. and the motor has a Inverter Duty rate of 10-90 HZ So I eliminated that.
I have temp wired directly between the output of the drive to the motor to eliminate any wiring issues.
The motor is a Bodine Motor "pacesetter" Inverter duty motor wired for 460.
And at 16 HZ you are getting 460 in and 120-130 ish volts out, which matches my math as appropriate (460/60 = 7.60) ------ 16 hz X 7.6=121.6 volts
Any ideas?