Why 5V encoder is used instead of 24V if pulse freq is high
AB2005
Nov 2006
Lahore
318
Hi;
I have noticed that at our machines, when pulse frequency of encoder is high, OEM uses 5V encoders instead of 24V. What could be the reason?
Improved noise immunity. 5vdc TTL vs 24vdc HTL design. With TTL you have A and B pulse along with the inverse signal (negated, A' and B'), and you can evaluate them against each other. With HTL you only have A and B.
Can't you have A' and B' on 24V encoders as well? What prevents that with HTL vs TTL.
A few things that come to my mind when looking at 5Vdc vs. 24Vdc.
First is transition time. The time it takes to go from 0 to 5Vdc is much shorter than the time it takes to go from 0 to 24Vdc. Also at 24Vdc you need a system that can swing 48V (0 to 24 / 0 to -24).
The other thing involves noise. Whenever you go from driving current to off you are collapsing a magnetic field which generates its own current which will be induced on any nearby wires and look like noise. The bigger the swing the larger the effect. This also has an impact on PCB size. The lower the voltage the closer you can have PCB traces to each other and the smaller you can make the PCB without getting cross talk or inducing noise onto the PCB's ground plane.
There are a lot of "little details" that add up most of which favor lower voltages.
My best guess would be TTL logic draws more current, therefore would be more noise immune.
And, yes, HTL or TTL can have compliments. TTL is 5v line drivers, and HTL is totem pole transistors. Same, only different! :)
Hello, I'm helluvawreck and I hope that someone can help me with this problem or at least point me in the right direction. My company has...
10,341
I have an application using an incremental encoder and then I convert it to degree (0-360) using calculation program. For a while, the calculation...
233
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
18
960
Dears, i am trying to change the series of encoder from A to B, but the program do not has this option (Rslogix5000, 20.06 the old encoder was...
200
Hi all, I am working with an incremental encoder (ABZ signals, 360 ppr (so 1440 counts per rev)) to replace the existing "manual" encoder wheel I...
51
2,559