I have been asked to see why an A500 VFD is not changing Hz despite the fact that I am getting the 4-20ma signal from our Honeywell loop controller on one of our boilers. I am completely unfamiliar with Mitsu drives and have reviewed the documentation yet am unclear on the setting range of 0-99,9999 for activation of the AU signal. This VFD is controlling an Overfire blower on one of our boilers so I am hesitant to just go changing things as one might imagine. My suspicion is that someone has clamped the max Hz or inadvertently turned off the Analog current signal in Par. 184 of the drive.
 
parameter 184 That should be at 4, this is rarely changed, Look at parameter 73 this selects the type and check terminals AU & SD are linked this is for 4-20ma

A500.png
 
Thanks for the heads up. Yes when looking into the parameter settings 73 denotes 0-5/0-10v selection. No mention of 4-20 ma signal.
 
If I remember correctly the parameter is a setting 0-10 or 0-5v so does not apply to 4-20ma, check parameter 79 it may be set for so only speed change from dial PU operation
 

Similar Topics

Hello everybody. I encountered a problem - I don’t know how to update the firmware on the Mitsu MR-J5-40G-N1 (ethercat) servo amplifier. My...
Replies
2
Views
265
Hello to Mitsubishi Electric experts. I have been tasked with developing an application that gets data from a MELSEC application, using MX Sheet...
Replies
2
Views
1,214
This is my first on the job exposure to messing about in a PLC with a PC. So far it hasn't gone too bad but I'm having a problem and it all...
Replies
9
Views
2,599
Hi all... help on Ethernet comm, between builtin EthernetQ03UDE to Laser Marker I'm using sp.socopen i cant open the port... is there any command...
Replies
4
Views
2,274
Hello all, this time is my question somehow theoretical, but with high practical impact. Let asume we have simple program and we have to...
Replies
6
Views
2,267
Back
Top Bottom