Studio5000 Requires Password to Open?

Join Date
Apr 2018
Location
Lincoln
Posts
3
I've loaded my application onto the HMI PC as required for this particular job but when I go to open the Controllogix v30 (Studio 5000) on said PC it asks me for a Factorytalk user name and password. Its not associated with the Controllogix program as it only requires this step when opened on this particular PC. Any ideas?
 
I've ran into similar behavior when renaming a computers hostname after installing newer Rockwell products.

There are typically 2 steps that resolve this. Run the "FactoryTalk Directory Configuration Wizard" found in Start > All Programs > Rockwell Software > FactoryTalk Tools. Or repairing FactoryTalk Services platform.
 