That is the load to all outputs it only shows 1 in other words all outputs sink or source the outputs are not isolated so only one supply can be used
for example the supply to the loads can be 0 or 24v dc or 240v ac (well any voltage) but as the relays are all common together you cannot mix voltages.
So you can for example put 24v DC on COM each output then goes to the load i.e. a contactor (A1) which have A2 to 0VDC