Good. ,how to connect the relay outputs to the CJ1W-OC211 card ?
IMG-20230128-095748.jpg
 
in terminal (Com) I have to connect the + 24v dc or mass (GND) ?

I want that when I activate output 0 or output 1 or any other output to have 24 V dc on that same output when it is active
 
That is the load to all outputs it only shows 1 in other words all outputs sink or source the outputs are not isolated so only one supply can be used
for example the supply to the loads can be 0 or 24v dc or 240v ac (well any voltage) but as the relays are all common together you cannot mix voltages.
So you can for example put 24v DC on COM each output then goes to the load i.e. a contactor (A1) which have A2 to 0VDC
 
The diagram on the card is quite clear - do not know why you have a problem. Connect 24 VDC + to both commons. Then connect the outputs to the 24 VDC + on your relays. Connect 24 VDC - to the other side of the relay coils.
 

Similar Topics

I have PLC Omron CJ2M with OD211 module. I want to use the pulse output and PWM output and this module. But i confuse how to activated this, i...
Replies
0
Views
106
Hello everyone, I would like advice on the setup below: CJ2M PLC: 192.168.10.01 (Subnet: 255.255.255.0) ETN21 - 192.168.20.1 (Subnet...
Replies
6
Views
1,859
Hello, I have an installation with an omron plc CP1L with a CJ1W-CIF12 module connected to eight omron MX2 drivers. I use the bus to modify the...
Replies
2
Views
2,147
Hello all, has anyone configured before 2 CJ1W-ETN21 in a single rack? I am trying to put 2 units of ETN21 couple with my CJ2M-CPU33 to act like...
Replies
1
Views
1,269
Dear All, I want to use a 4-20mA output from Omron AO module, so I did the following configuration: PLC used CJ1M-CPU22, rack 00 CJ1W-AD041, rack...
Replies
13
Views
4,963
Back
Top Bottom