Can a helpful soul double check this click program for bugs?
Aljubovic
Jan 2023
Louisville, Ky
88
Hello. I have been working on my first plc project for a while now. I just ordered all the parts that I need and before I did that, I created the program in do-more designer and simulated it. After debugging it the best I could and everything in the simulation worked, I transferred it all over to the click programming software so when my plc arrives, I can quickly start testing it.
This program is used to make an automated hydrostatic pressure testing unit for industrial hoses and has 4 devices.
1. pressure transmitter, 4-20mA, 0-2000psi
2. 3/2 Solenoid valve (for air supply cut off)
3. hydraulic solenoid valve (when overpressure detected, this will open and relief water pressure in hose)
4. ip current to pneumatic transducer, 4-20mA, 3-120psig
How it works is an operator will connect a hose to the system, then they will type in a pressure setpoint at which the hose will be tested at and also a time for how long to be held at that pressure. It does this by outputting the proper psi in the ip transducer to get the correct pressure output (Let's say the setpoint is 1000psi, the transducer would have to drive the pump with around 60-64 psi. The exact amount is calculated and then the ip transducer slowly ramps up to that pressure and holds it for the duration of the test. In this program the fluid supply valve and the pressure relief valve are manual, so when the operator presses the start button, a message appears on screen, they first need to open the fluid supply valve and wait for the hose to fill up with water, once water comes out the end of the hose (no more air inside the hose) the operator will close the relief valve, then they will press the okay button on the message that appeared on the hmi.
When the pressure test is done a message appears on screen to close the fluid supply valve and open the relief valve on the hose. Pressure will start dropping to 0 and then the program will reset.
If you want to actually simulate the program you will need to open data view in do-more and add in all pushbuttons, messages and setpoints to see what the program is doing. There are too many messages and outputs that I do not expect for anyone here to understand how this program fully works.
The do-more designer program has comments on most of the rungs to show what each one does.
Let me know if anyone finds any bugs, or rungs that will not work in my program for some reason.
Any help is appreciated. I will post the program for do-more and click down below.
Edit: There are more devices like hmi and mechanical devices, but I just put the main input and output devices. I will be using a c-more EA9-T6CL-R hmi.
Not run it but a quick look there are a few comments, I agree with splitting programs but I think you have gone too far.
First of all, a call to first scan, why not just put that in the main routine, the seperate call to the timers this makes things harder for others & possibly you, your monitoring the main program & a rung with a timer contact is not going true, so you have to go to the program with timers to see what's happening.
I do agree with seperate I/O mapping as this makes it easier to simulate as is the simulation program, Get rid of most of the NOP's it make sit look messy.
perhaps leave a couple as I know the editor is awful & just inserting lines seems very poor.
You seem to be copying data from one register to another many times it is difficult to follow.
I noticed C63 "Start Pumping" only seems to be reset on a Reset PB, Is this correct ?. what about normal end of the process ?.
No comments on some rungs so it would help a little more to add a bit more detail.
You also have a load of reset coils without them being set, also noticed a couple where you have an OUT coil but also reset of that coil, it should not need it, for example if you have logic that turns on a coil (not reset) then adding a reset will only reset it until the next scan because the logic is true so turns it on again, on the same issue, if the logic driving the coil is false then no need for reset.
I think a lot of your problems are because the amount of programs you have split it into, it has become so fragmented that you have lost your way a bit.
@parky Yes I should put the first scan into the main routine, but all other subroutines have a purpose and I can understand what each program is doing. Everything is very disorganized but it all works if you simulate it. I am just very worried about testing it in the real world because of accuracy and small errors that might arise.
The start pumping and many other timers, messages, and outputs are all reset with a reset pb. If ANY message appears on the screen the operator has to acknowledge it first and then hit the OK button on the message. This applies to every single message that will be displayed on the hmi (except 2 messages). Whenever the program is started, it will always end on some message display. This can be an error message, overpressure message, test passed message, and so on. Every single message has an OK button and it will reset the whole system back to 0. For the normal end of the process either a test passed or failed message will be displayed, when the operator presses OK the system will be reset to state 0 and everything else will be reset too.
Most of the reset coils are all for the messages and pushbuttons, I tested this program a month simulating it in do-more and everything worked properly. The system reset button is used to reset any messages, outputs, pb at the end of a test or when something goes wrong.
Since I am using a manual fluid supply valve and manual relief valve for when nothing goes wrong I have to display a message every time the system is ready to start the test and for when the system is ready to depressurize. So when the operator presses the start button a message is displayed to follow these steps (open relief valve, open fluid supply, wait for water to come out, close relief valve, and once completed he will push the ok button on the hmi. There are rungs that are always on that check if the system is building pressure and also a max pump to sp time, so if the operator does not do this and the system does not build pressure it will display an timeout message and the system will HAVE to be reset using the system_reset_pb
I understand that the program is very disorganized and there is a lot to look at, but running the simulation has given me good answers. I just hope that it will work using the real devices.
What rung did you see a load of reset coils without them being set?
Also I thought that with each scan that each subroutine was checked? All of my timers in do-more worked as the program went through each step. Not sure what you mean by this "your monitoring the main program & a rung with a timer contact is not going true, so you have to go to the program with timers to see what's happening" because all of the timers in do-more worked as I ran the simulation.
Are you saying that my timers wont be scanned if another subroutine is being scanned?
because the timers work at all points in the program if you simulate it the click is almost an exact copy of the do-more program so I think it will work the same too
Anyway there is too much for me to explain and because this is my first program it is very disorganized. My best bet would be to wait for the parts to arrive and slowly test each one.
The HMI program, as for testing I cannot as I do not have the HMI program so very difficult to run it.
see screenshot regarding the two I found without really looking.
@parky
Oh, thank you for noticing that. I copied (or at least tried to copy) the entire program that I made in do-more into the click program. I guess I missed something very important, the system would have not started pumping to sp at all if this one set command is missing.
A set command for start pumping is supposed to be in 20 states, rung 6, once on step 40 and psi has not dropped after starting the pump, pump_to_sp is set which starts a timer, that timer sets on ready_to_pump in 40 pretest pressure rung 1 which turns on start pumping. Start pumping is connected to 40 pretest pressure rung 4 and 5, which ramps the current to pneumatic transducer up to sp.
Now that I realize it I don't even need rung 1 (the start pumping output), it is just an extra command. I could just put ready_to_pump on 40 pretest pressure rung 4 and 5 instead.
Thanks for making me realize a crucial mistake in the program.
Also, I forgot to delete the Air out timer. This was used when I had a solenoid operated fluid supply valve, now that I have a manual one this is not used anymore.
As you seem to be having some Manual intervention one suggestion is that rather than setting bits for displaying messages on the screen use the multistate text indicator, set it as an integer rather than bits, add the messages giving each message a number based on the Sequence variable, this way it will automatically display the text for each sequnce.
For example:
When sequence =
0 "System IDLE"
10 "Fit Test piece & Acknowledge"
20 "Pressurising System"
30 "........
40 "......
& so on.
This way although you may have extra steps it is a way of showing the current state & giving the operator instructions on what to do.
Even if some steps you do not need to change the text just repeat it for the sequence number.
This means you do not have to set/reset bits it works off the sequence number.
one thing i did notice in the program is a alot of math for analog
the click plcs have the analog inputs alrady scaled
example - 4-20ma input scaled to -30 - 50 Celcius - the plc internally does that math for you when settings up the input you add the scaling and its done for you already
@Juddge: yes, but there has been a lot of input from other posters on a previous post on this system, like most of us we all have our way of doing things, & some have indicated that by scaling with the use of perhaps the HMI on a setup or engineering page means it is easy to re-calibrate sensors rather than have to change the fixed factors in the PLC, I sort of agree in this case it is probably not worth it as less than a couple of sensors seems a little pointless, could be a problem with people messing with it without a proper understanding we all know it is not long before operators find the engineering password.
The OP is still on a learning curve & it gives them ideas, however, sometimes these ideas are taken to the extreme. I hope the OP reads all the posts & makes his own judgement on what is nice to have & what is practical which will depend on the application.
Yup, I have finally gotten to the point where I tested all of my devices. I changed the Program just use analog input scaling and output scaling, so now my pressure transmitter will automatically be converted to units of psig and also my pressure transducer will output the correct psi as I input it. If something breaks and reads a wrong psi or number it will cause errors in the program and someone will have to notice, then I will go into the program and change some values and scaling is complete again.
I got to test out the pressure transducer and transmitter and they work perfectly, after plugging in my solenoids and an air supply to the transducer just to test it out, the program all works as it should in the test, the valves open when they should and also most importantly my pressure transducer ramps up in psi evey second, and I can change the scale factor and it will change how fast it builds pressure. Now I am waiting for pipes and mounting tools to actually start setting it up on the pump. Everything should work fine unless I accidentally break something, my next step after I complete this project is to try and use advancedhmi so I can set up a computer instead of an HMI to the system
Glad it's getting there, I did try the version in Do More but it's a bit of a poor simulator either that or I'm a novice with that one, at one point it was changing one of the variables quite fast got annoyed with it in the end so never went any further.
Hi guys, If you've ever lost the box your software came in (which I do all the time), and need to find the license code for backup purposes, this...
3,230
i have an application that involves over 30 AB Powerflex 70's and 6 AB Powerflex 700's all on ControlNet. this is my first controllogix...
6,218
Is it just me or are Technical Help desks not worth the price of the phone call? Twice last week I had cause to phone Mitsubishi technical help...
17
5,782
What is the simples way to do a double click of a button in a ladder logic. New here and I hope this has not been asked before.
22
445
Hi All, I'm keep getting double quotes in between selections rather than the beginning and the end. Here's the script and please help to find...
774