Powerflex 525 - Using Start and Stop Pushbuttons

Cydog

Member
Join Date
Feb 2018
Location
Maryland
Posts
313
Good Morning ,

I would like to start a Powerflex 525 with a N.O. Start Pushbutton , and when the N.O. Start Pushbutton is released I would like the motor to stay running till I press the N.C. Stop Pushbutton.

I guess this is considered a 3 wire Start/ Stop ? I wired it up like a normal
start / stop , and selected P46 to 2 ( DigIn TrimBlk ) , and the motor will only run as long as I keep the Start Pushbutton pushed in .

Only option to just put a relay with a hold in circuit ?

Thanks so much in advance ,
 
The digital input you are using must be configured for 3-wire control. Change t062 from the default 48 (2-wire forward) to 49 (3-wire start).
 
Thanks , Plvlce . I changed it to 49 , and it did not work at all after that. Any other options you can think of ?

Thanks so much.
 

Similar Topics

After replacing the 70 with the 525, the PLC can read from the drive and recognizes it as online, but no commands are being listened to. PLC is...
Replies
1
Views
545
Hi, I have a potentiometer connected to a siemens micromaster 440 to control a servo motor speed and they are not connected to any PLC. Now, I am...
Replies
9
Views
4,018
Good Morning , I have a quick question about the Powerflex 525 embedded ethernet drive. I'm using a CompactLogix 1769-L18 and using Ethernet...
Replies
2
Views
1,745
Good Morning , I'm building a control panel with PowerFlex 525 drives. I have black wire for the 480 vac , red for 110 vac , blue for 24 vdc...
Replies
7
Views
2,895
Good Morning , I know this is a higher expense , but I would like to keep 7.5 HP PowerFlex 525's in stock . I am doing a machine upgrade . I...
Replies
6
Views
2,774
Back
Top Bottom