Guys,
I have this remote rack communicating with a SLC 5/04. There are several "Analog" output cards in this RIO that are being used to control VFD's on blower fans through a 4-20ma signal.
I have one of these cards that channel 3 is not varying the 4-20ma signal going to one of the VFD at all.The value is always 4.36ma
.
I already confirmed that the 1746-NO4I card is good by doing a swap with another one.
I also checked the PLC code to make sure that there was no issues in it.
Do you guys think that the actual rack for this RIO could have a problem which affects that particular channel?
Also, the VFD (Allen-Bradley 160 SSC) always display 50HZ in the front screen even do the 4-20ma signal is not working. I checked all parameters against other equal VFD's that are working and I can not find any differences between them.