plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old October 22nd, 2018, 06:25 AM   #1
bitmonkey
United States
bitmonkey is offline
Types of analog, when to use which one?
Hi Guys,
I'm wondering if there are applications where 0-20mA ( 0r 4-20) might work better, or be more appropriate than 0-10v?
I have noticed that with some of my analog inputs that I seem to get more noise on the 0-10v than I do on the 0-20mA circuits, especially around the low end of the range. Even when my mA signal wire is unshielded, and the 0-10v signal is shielded. I've tried it both ways, with no significant improvement.
I guess I'm looking for a pros and cons list comparing 0-10v to 0-20mA?
__________________
I want to die peacefully in my sleep, like my grandfather, not screaming in terror like his passengers.
Old October 22nd, 2018, 06:33 AM   #2
James Mcquade
United States
James Mcquade is offline
as you have already noted, the 4-20 ma signal is less subject to noise.
this type of loop is current dependent, not voltage.
the 0-10 volts input is voltage dependent and is subject to noise from vfd's motor wiring, and other sources.
if I am incorrect, someone please correct me.
james
Old October 22nd, 2018, 06:44 AM   #3
gclshortt
Canada
gclshortt is offline
gclshortt's Avatar
https://automation-insights.blog/201...0v-vs-4-20-ma/
http://www.plctalk.net/qanda/showthread.php?t=37904
http://www.plctalk.net/qanda/showthread.php?t=91443
+1 James
The above links may help you out. If I had a choice it would be 4-20mA.
Regards,
__________________
Garry
https://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
Old October 22nd, 2018, 07:28 AM   #4
Tom Jenkins
United States
Tom Jenkins is offline
Tom Jenkins's Avatar
Another advantage of 4-20 mA transmitters is the availability of many in 2-wire loop powered configurations. Voltage outputs are 3-wire or 4-wire.
Old October 22nd, 2018, 07:35 AM   #5
roxusa
United States
roxusa is offline
Another advantage I've found is the 4-20mA is the same for a sensor at 100' of cable vs 10' of cable which makes setting the scaling up nice. the 0-10v you would have to account for the voltage drop.
__________________
B.Pedersen
if you are going to assume, assume you're wrong.
Old October 22nd, 2018, 08:06 AM   #6
mk42
United States
mk42 is online now
Another advantage is that 4-20 gives you easy diagnostics on a broken wire. If it reads 0, the PLC knows that theres some kind of error.
Old October 22nd, 2018, 08:36 AM   #7
BryanG
United Kingdom
BryanG is offline
It is an old analogy, but still true.
If you have a water pipe and you run water through it there will be a pressure drop down the pipe, so here pressure is the equivalent of volts. The volts at one end can be different than the volts at the other.
But the flow of water going in one end has to be the same as the flow going out of the other, here flow rate is current. The current at one end has to be the same as the current at the other.
It isn't a perfect analogy and as frequency increases you can get capacitive effects so that the pipe can briefly store current.
What if the pipe expands or springs a leak? The answer to those one will cost you extra.
__________________
Knowledge is power, share the knowledge.
Old October 22nd, 2018, 09:13 AM   #8
Tom Jenkins
United States
Quote:
I hear that a lot, but that is really less often a problem than it is usually thought to be.
Let's say your PLC input impedance is 150 k-Ohm. At 10 VDC the current is only going to be 67 micro-Amps. If you have 1,000 ft. of #24AWG your voltage drop at the input is only about 2 milli-Volt. That's negligible.
Old October 22nd, 2018, 09:21 AM   #9
danw
United States
danw is offline
danw's Avatar
0-20mA only applies to a 4 wire device, like an analog output on a PLC, where the power to run the output electronics is supplied by the PLC.
4-20ma devices use the 3.6mA of the loop current 'below' the 4.0mA signal 'zero' threshold to power the device electronics. That's why they're 2 wire devices. The same two wires going out to the field instrument carry both the device power and the signal.
Old October 22nd, 2018, 02:09 PM   #10
mass89
United Kingdom
mass89 is offline
4-20mA everyday, suitable for very long runs, often 2-wire is available, 4mA starting point allows you to easily determine signal loss over low signal (low level for instance)
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Using non-isolated Analog I/O on S7 1215C CPU RonJohn LIVE PLC Questions And Answers 5 September 5th, 2014 08:18 AM
Experts on Schneider Electric TM2AMM6HT! dwpang LIVE PLC Questions And Answers 30 May 26th, 2014 02:21 PM
Analog Signal Scaling Types mosama LIVE PLC Questions And Answers 5 March 18th, 2014 10:47 PM
ML1100 analog input help kbradray LIVE PLC Questions And Answers 6 December 11th, 2007 05:13 PM
analog input SIMATIC S7-200, EM235 sarac LIVE PLC Questions And Answers 1 October 26th, 2006 03:32 AM