Types of analog, when to use which one?

Hi Guys,
I'm wondering if there are applications where 0-20mA ( 0r 4-20) might work better, or be more appropriate than 0-10v?
I have noticed that with some of my analog inputs that I seem to get more noise on the 0-10v than I do on the 0-20mA circuits, especially around the low end of the range. Even when my mA signal wire is unshielded, and the 0-10v signal is shielded. I've tried it both ways, with no significant improvement.
I guess I'm looking for a pros and cons list comparing 0-10v to 0-20mA?
__________________
I want to die peacefully in my sleep, like my grandfather, not screaming in terror like his passengers.
  Reply With Quote
Old October 22nd, 2018, 07:33 AM   #2
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,238
as you have already noted, the 4-20 ma signal is less subject to noise.
this type of loop is current dependent, not voltage.

the 0-10 volts input is voltage dependent and is subject to noise from vfd's motor wiring, and other sources.

if I am incorrect, someone please correct me.

james
  Reply With Quote
Old October 22nd, 2018, 07:44 AM   #3
gclshortt
Member
Canada

gclshortt is offline
 
gclshortt's Avatar
 
Join Date: Dec 2014
Location: Cobourg
Posts: 2,653
https://automation-insights.blog/201...0v-vs-4-20-ma/

http://www.plctalk.net/qanda/showthread.php?t=37904

http://www.plctalk.net/qanda/showthread.php?t=91443

+1 James
The above links may help you out. If I had a choice it would be 4-20mA.
Regards,
__________________
Garry
https://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
  Reply With Quote
Old October 22nd, 2018, 08:28 AM   #4
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,915
Another advantage of 4-20 mA transmitters is the availability of many in 2-wire loop powered configurations. Voltage outputs are 3-wire or 4-wire.
  Reply With Quote
Old October 22nd, 2018, 08:35 AM   #5
roxusa
Lifetime Supporting Member
United States

roxusa is online now
 
Join Date: Nov 2008
Location: NJ
Posts: 646
Another advantage I've found is the 4-20mA is the same for a sensor at 100' of cable vs 10' of cable which makes setting the scaling up nice. the 0-10v you would have to account for the voltage drop.
__________________
B.Pedersen
if you are going to assume, assume your wrong.
  Reply With Quote
Old October 22nd, 2018, 09:06 AM   #6
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,938
Another advantage is that 4-20 gives you easy diagnostics on a broken wire. If it reads 0, the PLC knows that theres some kind of error.
  Reply With Quote
Old October 22nd, 2018, 09:36 AM   #7
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,287
It is an old analogy, but still true.

If you have a water pipe and you run water through it there will be a pressure drop down the pipe, so here pressure is the equivalent of volts. The volts at one end can be different than the volts at the other.

But the flow of water going in one end has to be the same as the flow going out of the other, here flow rate is current. The current at one end has to be the same as the current at the other.

It isn't a perfect analogy and as frequency increases you can get capacitive effects so that the pipe can briefly store current.

What if the pipe expands or springs a leak? The answer to those one will cost you extra.
__________________
Knowledge is power, share the knowledge.
  Reply With Quote
Old October 22nd, 2018, 10:13 AM   #8
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,915
Quote:
Originally Posted by roxusa View Post
Another advantage I've found is the 4-20mA is the same for a sensor at 100' of cable vs 10' of cable which makes setting the scaling up nice. the 0-10v you would have to account for the voltage drop.
I hear that a lot, but that is really less often a problem than it is usually thought to be.

Let's say your PLC input impedance is 150 k-Ohm. At 10 VDC the current is only going to be 67 micro-Amps. If you have 1,000 ft. of #24AWG your voltage drop at the input is only about 2 milli-Volt. That's negligible.
  Reply With Quote
Old October 22nd, 2018, 10:21 AM   #9
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,819
0-20mA only applies to a 4 wire device, like an analog output on a PLC, where the power to run the output electronics is supplied by the PLC.


4-20ma devices use the 3.6mA of the loop current 'below' the 4.0mA signal 'zero' threshold to power the device electronics. That's why they're 2 wire devices. The same two wires going out to the field instrument carry both the device power and the signal.
  Reply With Quote
Old October 22nd, 2018, 03:09 PM   #10
mass89
Member
United Kingdom

mass89 is offline
 
Join Date: Oct 2017
Location: England
Posts: 15
4-20mA everyday, suitable for very long runs, often 2-wire is available, 4mA starting point allows you to easily determine signal loss over low signal (low level for instance)
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Using non-isolated Analog I/O on S7 1215C CPU RonJohn LIVE PLC Questions And Answers 5 September 5th, 2014 09:18 AM
Experts on Schneider Electric TM2AMM6HT! dwpang LIVE PLC Questions And Answers 30 May 26th, 2014 03:21 PM
Analog Signal Scaling Types mosama LIVE PLC Questions And Answers 5 March 18th, 2014 11:47 PM
ML1100 analog input help kbradray LIVE PLC Questions And Answers 6 December 11th, 2007 06:13 PM
analog input SIMATIC S7-200, EM235 sarac LIVE PLC Questions And Answers 1 October 26th, 2006 04:32 AM


All times are GMT -5. The time now is 02:33 PM.


.